Hi ebow,
Yes, you were ok working it out to the value given in the regs/ test paper you were looking at, I had read quickly through the posts and mentioned the correction factor.
If you were doing a PIR or working it out for real, you would need to apply the 80% rule to the values given in BS7671 book to take account of the max temperature of the cable, to see if it complies or not.
See: Zs values in Table 41.3 of BS7671 (see APP 14 in BS7671).
This was entirely my fault, I hadn't read the whole of the thread properly, and did not realise what you were asking, sorry I did not mean to confuse you.
does the principle of determining the max Zs not apply now?
Yes, you were ok working it out to the value given in the regs/ test paper you were looking at, I had read quickly through the posts and mentioned the correction factor.
If you were doing a PIR or working it out for real, you would need to apply the 80% rule to the values given in BS7671 book to take account of the max temperature of the cable, to see if it complies or not.
See: Zs values in Table 41.3 of BS7671 (see APP 14 in BS7671).
This was entirely my fault, I hadn't read the whole of the thread properly, and did not realise what you were asking, sorry I did not mean to confuse you.