WHen doing the continuity of a ring main and the cpc is 1.0mm should the reading be 1.25 times the R1 or Rn value. And 1.75 if its 1.5mm?
 
Whats RT refering to? and is A1 say the size of cpc csa? and A2 the csa of the line conductor?

RT represents the total, in this case, the R1&R2.

A1 is the CSA of R1, and A2 is the CSA of R2.

For example... say you have an R1&R2 of 0.85ohms and you want to determine R1, Rn and R2. In theory we can determine Rn from obtaining R1's value.

So..

R1&R2 = 0.85 ohms..

R2 = (RTXA1)/(A1+A2) = (0.85x2.5)/(2.5+1.5) = 0.53 ohms

R1 = (RTXA2)/(A1+A2) = (0.85x1.5)/(2.5+1.5) = 0.32 ohms

So we have (R1) 0.32 ohms + (R2) 0.53 ohms = 0.85 ohms (R1&R2)
 
RT represents the total, in this case, the R1&R2.

A1 is the CSA of R1, and A2 is the CSA of R2.

For example... say you have an R1&R2 of 0.85ohms and you want to determine R1, Rn and R2. In theory we can determine Rn from obtaining R1's value.

So..

R1&R2 = 0.85 ohms..

R2 = (RTXA1)/(A1+A2) = (0.85x2.5)/(2.5+1.5) = 0.53 ohms

R1 = (RTXA2)/(A1+A2) = (0.85x1.5)/(2.5+1.5) = 0.32 ohms

So we have (R1) 0.32 ohms + (R2) 0.53 ohms = 0.85 ohms (R1&R2)

Thanks so using your formulars. I have worked out that when checking the continuity of ring mains i need to times my r1 value by either 1.67 for 1.5mm cpc or 2.5 for 1.0mm cpc

so an r1 reading of 0.20 with 1.5mm cpc should provide me with an reading of 0.33 i'll see how these work on site tomorrow.
 
Rn will allways be the same as R1 because they are the same CSA if you have a difference of more than 0.02 ohms you have to investigate this. That is providing the Neutral is the same legnth as the Line conductor, which in a ring it will be.
 
Rn will allways be the same as R1 because they are the same CSA if you have a difference of more than 0.02 ohms you have to investigate this. That is providing the Neutral is the same legnth as the Line conductor, which in a ring it will be.

0.05 Ohms is the accepted difference.
 

Reply to Calculating R2 from R1 and RN in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
252
  • Question
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
Replies
2
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top