Calculating R2 from R1 and RN | Page 2 | on ElectriciansForums
Discuss Calculating R2 from R1 and RN in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
indirectly, to be precise , rocker.
i think what rocker means is divide the csa of the line conductor by that of the cpc to get the ratio of their respective reistances.
So how would that work if we only had an (R1&R2) and not an individual R1 or R2 value?
I'll think this over in the morning.. sleepy time now me thinks.
easy one . say we have R1+R2 = 2.35 ( hypothetical figure )
R2 = 1.67 x R1 ( 2.5/1.5mm )
so R1 + ( 1.67xR1 ) = 2.35
( 2.67xR1 ) = 2.35
R1 = 2.35/2.67 = 0.88
R2 = 2.35 - 0.88 = 1.47
( or R2 = 1.67 x 0.88 =1.47)
Reply to Calculating R2 from R1 and RN in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
    • Friendly
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Also,if you had a duel box with a lighting cct on one side you would get a false reading.