Calculating Voltage Drop | on ElectriciansForums

Discuss Calculating Voltage Drop in the UK Electrical Forum area at ElectriciansForums.net

Cookie

-
Joined
Jul 11, 2019
Messages
675
Reaction score
126
Location
Earth
How is voltage drop of a circuit normally calculated in the UK? And why are wires 16mm2 and under listed as a single unit, but 25mm2 and over in R, X and Z? How do I work with Z?
 

Attachments

  • [ElectriciansForums.net] Calculating Voltage Drop
    wire.jpg
    130.3 KB · Views: 14
in the UK we use tables showing mV/A/m for different cable sizes. e.g. if we have a cable 50m long, 20A, and the table shows 7mV/A/m, then VD = (7 x 50 x 20)/1000 i.e. 7000mV or 7V.
 
For small cables at 50Hz, the ohmic resistance dominates, so it is not important to consider the DC resistance and AC impedance separately. A single figure is used for all applications.

For larger cables with lower resistance, the inductive reactance starts to become significant on AC, so the voltage drop arising from each effect, and their vector sum, is given. For DC, the r figure alone would be used. For AC, the impedance. By tabulating both the reactive and resistive contributions, the total drop for a load of known non-unity pf can be calculated (where the drop is displaced in phase from the line voltage) for greater accuracy.
 
But even for small cables, doesn't load power factor effect voltage drop considerably? Does DC resistance or AC resistance give the worst figures vs AC reactance (Z)?
[automerge]1575993418[/automerge]
Here is the NEC's Table 9. Reactance, even load power factor when known is taken into account for smaller conductors down to 2.08mm2.
 

Attachments

  • [ElectriciansForums.net] Calculating Voltage Drop
    table 9.jpg
    473.9 KB · Views: 10
  • [ElectriciansForums.net] Calculating Voltage Drop
    Table 9 #2.jpg
    109.7 KB · Views: 8
Last edited:
You make a good point. I am not sure why the NEC and BS take different approaches here, and looking at the NEC table the ratio is greater than I thought on small circuits (i.e much smaller than the crossover point around #2). I would like to plug some numbers in and see how much impact it has but time doesn't permit. @marconi will be along presently, he often seems to have more patience for number crunching than I do!
 
Last edited by a moderator:

Reply to Calculating Voltage Drop in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
I am working on a RV Park and I have a question. I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and...
Replies
0
Views
480
  • Question
these are usually MOV’s metal oxide varistors or sometime spark gaps , these change there resistance with voltage,im fairly sure the lower voltage...
Replies
1
Views
391

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top