How is voltage drop of a circuit normally calculated in the UK? And why are wires 16mm2 and under listed as a single unit, but 25mm2 and over in R, X and Z? How do I work with Z?
 

Attachments

  • wire.jpg
    wire.jpg
    130.3 KB · Views: 24
in the UK we use tables showing mV/A/m for different cable sizes. e.g. if we have a cable 50m long, 20A, and the table shows 7mV/A/m, then VD = (7 x 50 x 20)/1000 i.e. 7000mV or 7V.
 
For small cables at 50Hz, the ohmic resistance dominates, so it is not important to consider the DC resistance and AC impedance separately. A single figure is used for all applications.

For larger cables with lower resistance, the inductive reactance starts to become significant on AC, so the voltage drop arising from each effect, and their vector sum, is given. For DC, the r figure alone would be used. For AC, the impedance. By tabulating both the reactive and resistive contributions, the total drop for a load of known non-unity pf can be calculated (where the drop is displaced in phase from the line voltage) for greater accuracy.
 
But even for small cables, doesn't load power factor effect voltage drop considerably? Does DC resistance or AC resistance give the worst figures vs AC reactance (Z)?
[automerge]1575993418[/automerge]
Here is the NEC's Table 9. Reactance, even load power factor when known is taken into account for smaller conductors down to 2.08mm2.
 

Attachments

  • table 9.jpg
    table 9.jpg
    473.9 KB · Views: 14
  • Table 9 #2.jpg
    Table 9 #2.jpg
    109.7 KB · Views: 12
Last edited:
You make a good point. I am not sure why the NEC and BS take different approaches here, and looking at the NEC table the ratio is greater than I thought on small circuits (i.e much smaller than the crossover point around #2). I would like to plug some numbers in and see how much impact it has but time doesn't permit. @marconi will be along presently, he often seems to have more patience for number crunching than I do!
 
Last edited by a moderator:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Earth

Thread Information

Title
Calculating Voltage Drop
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
Cookie,
Last reply from
Cookie,
Replies
13
Views
2,633

Advert

Back
Top