Yes quite often say for a downstairs lighting circuit and there as been an extension built. It can sometimes be easier to take a LINE/NEUTRAL/EARTH from the CU rather than perhaps destroying decor or taking boards up trying to take a spur of the circuit. Basically your using the MCB as a JB, As long as the spur is feeding lights on the same circuit. ie downstairs lights then it is done.
 
If the MCB is acting as a JB the the spur should only source 1 load, correct ? As also noticed 32a with three lines, i assume this to be 1 final ring circuit and 1 spur, if doing an R1 + R2 how do you test for the spur off the final ring circuit to take the highest reading ?
 
Look at reg 314.4 where it tells you that each final circuit must have its own individual way in a DB. So for the scenario I told you the downstairs lights which most likely be front room, hall, kitchen, etc and then a downstairs light in an extension that is all classed as a single final circuit as htey are all downstairs light. Which means when you isolate the MCB for the downstair lights, all the downstairs light will be isolated.

Appendix 15 tells us that you can take a single unfused spur double socket from each point in a ring or at the CU. If I found that you had an unfused spur via the CU I would do all my R1+R2, as per normal, at every socket on the final circuit, which is the ring and the spur, and whichever was the greatest value would be my R1 + R2 value, chances are it could actually be a socket on the ring rather than the spur socket, it would depend on the spur length.
 
sorry getting a little confused, if i'm doing a r1 + r2 for ring final circuit when taken out of the MCB, i would be doing the highest value but if a circuit has also been added but as a spur in the same MCB, what reading do i give for this spur and would it need to be take as R1 + R2 as a separate entity ? In theory 2 circuits for 1 MCB.
 
You would enter the highest r1 + r2 measurement onto the cert, whether that is the ring part or the radial spur part of the circuit. It is just the same as a spur from the middle of the ring, the mcb is classed as just another cable junction. If you were to split the ring at a plug socket for your measurements the spur off the MCB would be the same as any other spur off the ring, so therefore they should be classed as the same circuit because they originate from the same MCB. Hope this lessens the confusion.
 
Last edited:
You would enter the highest r1 + r2 measurement onto the cert, whether that is the ring part or the radial spur part of the circuit. They should be classed as the same circuit because they originate from the same MCB. Hope this lessens the confusion.
That will be the case when you come to the Zs test as well. You'll test the sockets on the ring and the spur and record the highest Zs on that one circuit on the cert.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
calculating Zs with only R2 reading
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
87
Unsolved
--

Advert

Thread statistics

Created
egginyourface,
Last reply from
Gazap,
Replies
87
Views
22,635

Advert

Back
Top