i could have done r1 + r2 but for some reason i decided not to o it...its the 1st and last and wont ever be doing this again. will be doing the r1+r2 method next time.

still feel that theres nothing wrong with it
 
For a PIR I have to say that in a commercial situation there are many times you can't do the R1+R2 test, that is why your schedule of results allows you to use a R2 only reading, in fact if you wished you can even do R2 for an EIC, but to be honest I don't think I would want to do just that.

R2 is your continuity of the protective conductor and if you can prove that throughout the circuit and do your Zs test then R1 + R2 for a PIR is perhaps not so critical.

It is to be remembered that the tester on a PIR decides with his experience and competency which tests are required, even the GN 3 in the PIR section only advises a Zs test at the origin of the installtion, at a DB, a socket outlet or the end of a radial circuit, so lighting circuits are pretty much not needed.

So if you know your R2 then yes in theory you could calculate your R1, but as in the age old question why would you want to
 
ok so what is the lenght? a line conductor in a light circuit may well be longer than the cpc , so you cant just say its 1.5 mm/1.0mm etc
and what resistances do all the switches have??
 
ok so what is the lenght? a line conductor in a light circuit may well be longer than the cpc , so you cant just say its 1.5 mm/1.0mm etc
and what resistances do all the switches have??

once again, these opinions of yours are warranted and any experienced competent person will take these into consideration. However they cannot be used to oppose the fact that by design or calculation, these methods are accepted.

This is going round and round in circles.
 
how can it be done though if you dont know the lenght?
the line conductor is not the same lenght as the cpc , this is why i say it is not possible
the op said he did an R2 reading and asked if could then work out the ZS, he cant is the only answer because he does not know the resistance of R1 and it cant simply be guessed.
design calcs dont come in to it , this was a live situation where all the values and figures are not available to calculate ZS.
 
how can it be done though if you dont know the lenght?
the line conductor is not the same lenght as the cpc , this is why i say it is not possible
the op said he did an R2 reading and asked if could then work out the ZS, he cant is the only answer because he does not know the resistance of R1 and it cant simply be guessed.
design calcs dont come in to it , this was a live situation where all the values and figures are not available to calculate ZS.

Yes you can, you will need to know the circuit length and the size of the conductors.

Read the whole thread, it helps..
 

Reply to calculating Zs with only R2 reading in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
Replies
2
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top