I need to calculate the Zs for a ring main that uses the metal conduit as CPC. I know that Zs = Ze + R1R2 but I only have an R2 reading as there is no wired CPC. Anyone got a clue?
 
Yes I have a multi function Megger. The Ze at the time of testing was way over the max allowed. So the local supply company have eventually repaired the supply 2 weeks later and PME'd it to get the reading down. I could therefore only do dead testing at the time and have no intention of going back to re-test every circuit now. I need to calculate all Zs readings from the new Ze and R1R2s
 
new/converted supply...new connected mains terminations ... how do you know the DNO hasn't got a bad connection?... you need to revisit to ensure new setup is correct.

You went to test a job ...it failed you called in DNO to rectify issue.

You now need to go retest .... cant see issue here - 2 separate invoices 1 for initial testing 2nd one for testing following supply upgrade.

Obviously its only the live tests to re-do and you can discuss with the customer the second testing will be a reduced cost visit.
 
So why are you altering your results, any remedial works are surely chargeable?

The DNO have done there bit, it's not upto the customer to ask for a retest and pay for it surely?

- - - Updated - - -

You issue cert saying not suitable for continued use, that's all they have paid for unless the remedially work is included I the price they are paying you.
 

Reply to Calculating Zs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top