I need to calculate the Zs for a ring main that uses the metal conduit as CPC. I know that Zs = Ze + R1R2 but I only have an R2 reading as there is no wired CPC. Anyone got a clue?
 
We are getting away from the point here. The school was closed for the holiday so was not in use and safety wasn't an issue. I dead tested R1R2s on all circuits with a view to calculating Ze's as is allowed in Guidance note 3. The Ze is now acceptable and I just need to know how to calculate the only circuit that doesn't have a cpc
 
You can't can you, you proved that in your opening post. Just in case you missed it

Zs=R1+R2+Ze

No you only have Ze

R2 only exists in your head.

So looks like a revisit at your expense if you want to reissue a cert with out actully proving anything yourself, which leaves you wide open for all sorts of problems in the future
 
Nice thought but it's a school and they ain't gonna pay twice

Either you haven't included or discussed your need to revisit with the school thus not quoted for it but in light of your findings and the issue of a failed cert' you now need to now confirm the new set-up is compliant and issue a post upgrade cert' whether the school likes it or not they will not have a satisfactory cert' unless they pay for a second testing ....as i have mentioned in my edit of my last post ... you should be liaising with the school about the this and explain that 2 thirds of the testing will not be required but you will need to redue the rest as the earthing system has been changed meaning all live previous values have now changed.


I don't see a problem here its standard practice I can only see an issue if you haven't informed the school throughout the testing and remedial about the change to any quoted work that the supply upgrade will have...
If they want a passed cert' you will need to do some retesting how will calculations show any issues that may be present regarding DNO work done?


If you have been back and got the Ze and guidance notes express you can now calculate all Zs values (not got my copy to hand and never needed to go down this route) then id still be inclined to take a few random tests of various circuits to back up your calcs are close to actual measured values ... if not then something could be amiss.
 
Last edited by a moderator:
I'm confused.

You have R2 reading (conduit).
Presumably, you have the measured RFC end to end resistances (r1,rn).
You have Ze following DNO fix.

All the ingredients are there for a calculated Zs.

Or have I misunderstood?
 
Nice thought but it's a school and they ain't gonna pay twice
Of course they won't, they expected a professional electrician to visit their premises and install an electrical system and to issue test certificates based on testing with instruments in regard to the works carried out. You didn't do your job properly and you need to eat humble pie and get back there and do the Job right, absolutely ridiculous, appalling in fact.
 
Go to the school talk to whoever you liaise with tell them you will be needing to take sample zs tests, i assume prior the DNO upgrade a majority of the circuits failed on Zs ..even if you calculate them all some may have other issues not related to the original poor earth and may be now borderline pass/fail even with your new calcs ... its circuits like these that need retesting .... your only going around doing random zs tests and ensuring the ones that are borderline by calc actually do pass.... a morning or a days work depending on school... go in on a sat' you charge for it job done where's is the problem.

Its seeming more like it not actually been a problem for a school to find a couple of hundred extras pounds and more like you hate doing it and trying to find excuses... even in these tight buckle times a school won't refuse if it stop them getting insurance .... i spent yrs working in them during hols and acted as Electrical Foreman and i cannot understand a school refusing to pay under your circumstances the extra time to do some sample tests.

Are you a company boss / self employed or is someone else pulling your strings and telling you you can't go back and to just calculate it? If the latter tell your boss from me he's a $%^$ÂŁ^$&^ XXXX%$^^& and to (*&^% > ***&^%$$ &^%% ---and if it gets stuck up there then tough titty.
 
Last edited by a moderator:
Of course they won't, they expected a professional electrician to visit their premises and install an electrical system and to issue test certificates based on testing with instruments in regard to the works carried out. You didn't do your job properly and you need to eat humble pie and get back there and do the Job right, absolutely ridiculous, appalling in fact.
Way too harsh and well off the mark there based on my reading of the OP.

Sorry if I'm wrong.

Sounds like you should spend less time hanging out with Glenn!
 
How can you give out electrical certs that demand an Earth Loop test carried out with a live supply , should have factored in a possible re visit within your pricing , if thats the issue , whatever that does not change anything your name is on them certs
 

Reply to Calculating Zs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top