Calculation of ZS

Hi guys am I right in saying that if the circuit in question is protected by rcd/rcbo then there is no need for the multiplier. (table 41.5) really unsure about this. Any help would be good I've got my 2394 written tomorrow I've pasted the practical and multiple choice.
 
Not sure what you mean.

If you mean the 0.8 correction factor for the temperature, it would hardly apply to 1,666Ω - would 1,333Ω be satisfactory for a circuit?

If you mean an RCD/RCBO means you can ignore the maximum Zs for the overcurrent protection device then - no, you are not right.
 
No I know you still have to check zs readings with those set in bs7671 I know that rot is 80% of regs readings. I'm talking about if cables are bunched or if temp is not 20degrees sorry for being unclear but iPhones and long explanations are a real bad mix
 
No I know you still have to check zs readings with those set in bs7671 I know that rot is 80% of regs readings. I'm talking about if cables are bunched or if temp is not 20degrees sorry for being unclear but iPhones and long explanations are a real bad mix

So is digging up threads that are 4+ years old!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
rapier,
Last reply from
Jamie198,
Replies
21
Views
31,004

Advert

Back
Top