the osg say's i can use 56m of cable of 1.0/1.0 installation method 103,101 e.tc. for lighting, on a radial at 6A. the mV/A/m is 44.
so 44x6x56/1000=14.7v that is 6% of lighting not 3%.
what am i missing
The resistance of a single 1mm2 copper conductor at 20oC is 19.5 mohm/m (possibly 18.1 in OSG) this gives a volt drop of 6.55 V over 56m at 6A. You may be looking at R1 + R2 values instead which are two conductors in series so your length would then be 112m.
Reply to calculation question in the Australia area at ElectriciansForums.net
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
The conductivity value stated on Wikipedia, etc, will be for pure crystal copper, not the annealed stuff with traces of oxygen and other elements...