Hi. Im looking for some advice when calculating submain cables.
Basically there is a new connection of 80Amps that is to be used for a dwelling and a small workshop. I had thought taking to a feeder box with one submain and then two feeds away into the buildings.
A direct run from dno to feeder box is 70m a preferred run would be 100m
25m into dwelling.
50m into small workshop.
I was told the volt drop wpuod need to be 3% from dno to end of lighting circuits.
My calculations are showing.
100m 95mm swa
25m 35mm swa
50m 35mm swa
But other firms have told the customer that they would use 25/35mm swa for the entire run due to diversity.
Even with divesity of the dwelling im coming up to about 45A for that alone.
Any advice would be most appreciated.
Thank you