I embarrassed that don't remember this but swallowing some pride is sometime good for a person. I am wiring a 3 phase in-line water heater and the manufacturer lists the current draw at 177A. at 480 volts, (144kw). Would that be per phase rating or would that be just the total. I was thinking it was just the total and i needed to calculate the phase current at 48kw/(480v x square root of 3)=58A. Unfortunately, I've started to doubt myself. Thanks for the help.
 
That would be the per-phase current, assuming when you say 480V you mean L-L so around 277V L-N.

144kW at 277V = 520A, so split over 3 phases you have 173A/phase.

That sure is a big heater! I'm guessing for a hotel or some industrial site?
 
Confirmed by the fact for a typical heater of that rating they suggest a 200amp 3ph breaker

144kw heater.PNG
 
That would be the per-phase current, assuming when you say 480V you mean L-L so around 277V L-N.

144kW at 277V = 520A, so split over 3 phases you have 173A/phase.

That sure is a big heater! I'm guessing for a hotel or some industrial site?
Thank you for your help. It is a pretty good sized heater. We use it to heat the water in a safety shower system.
 

Reply to Calculaton questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey so I need help understanding this question and understanding it in the NEC.The service to a multistory building is 277/480-volt, 3-phase...
Replies
4
Views
2K
Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
1
Views
408
Hi there im in training, but my question is using using a 3 phase 480v delta to 208/120 delta transformer 30kva and wiring it in reverse for 208...
Replies
1
Views
741
Hi, Sorry, lengthy post. Really only need to read the next sentence to be able to answer my question. The rest is what I have considered and...
Replies
0
Views
682
Hi All, First of all apologies for the potentially novice sounding question believe it or not I’ve been a qualified electrician for 10 years but...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top