Can an upstream fault cause an RCBO to trip? | on ElectriciansForums
Discuss Can an upstream fault cause an RCBO to trip? in the Australia area at ElectriciansForums.net
L
LlandrilloSpark
Fellas
Scenario - 1 main three phase board feeding 3 further three phase boards with each of those feeding 15 single phase boards containing only two final circuits each.
The fault is on the final circuits, ive tested the final circuits and all clear, can a fault on the distribution circuits upstream cause the RCBO to operate?
cheers
I've heard of sodium/mercury lighting switchgear like streetlighting causing RCD's to trip. Not sure if it's a harmonics issue or if some residual current devices are more prone than others.
It is my understanding that certain circumstances upstream of an rcd/rcbo can cause tripping eg voltage spikes, switching of large inductive loads. Are you confident that the rcbo is working correctly - what does a ramp test show and are you certain that nothing being used on the circuit in question is not allowing an earth leakage
Edit also heard the other day of walkie talkies causing rcds to trip.
Walkie talkies...."BREAKER...BREAKER"....lol........
nothing leaking to earth as the final circuits power 3 light fittings,2 leds, and 2 sockets only between them!, rcbo trips as 21mA, so i changed to a c type tripping at 27mA but i clamped the earth and under full load there isnt 2mA leakage, im just weighing up if i am going to have to test all the distribution circuits also
Hi llandrillo you are talking about an RCBO it trips on overcurrent like an MCB and on earth fault like an RCD. Don't concentrate on earth leakage it could be an insulation fault on the final circuit
I suggest start from scratch R1+R2, IR, polarity, Zs then function of the RCBO
Once you are convinced final circuit is OK then look upstream
An up stream fault can cause tripping but the usual cause is one of the up stream breakers tripping, which I think you’d notice. Are there any inductive loads being switched up stream?
went back today, everything fine since i changed a few accessories and the most troublesome room which tripped daily hasn't tripped since i changed the RCBO from a type b Eaton Mem tripping at 21mA to a Type c crabtree tripping at 27mA, i didn't change any lamps or accessories in that room, its very strange that only four rooms are effected, also that the distribution circuit supplying each room is on a different phase, so no one phase has a problem there.
One thing i did find though is that there is a three phase lift upstream, big motor, might cause the trip.
Reply to Can an upstream fault cause an RCBO to trip? in the Australia area at ElectriciansForums.net
Ye smaller board (containing the RCBO'S) will literally be next to the MEMSHIELD, And hence the 32A MCB be simply feeding power to a 32A RCBO I...
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...