Can anyone clear this up? | on ElectriciansForums
Discuss Can anyone clear this up? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Judd
Liverpool
Just carried out some small works in a ground floor WC, moved the position of a light and replaced it with a new one,
The circuit at the moment is protected by a 6A MCB, but lacks additional protection by means of a 30mA RCD for cables buried <50mm plaster. There's no bath or shower room on the circuit,
My supervisor has said it doesnt require RCD but ive heard conflicting opinons, Just filling out the minor works now,
Should I note the lack of additional protection in the comments or departures.
Thanks Judd
Existing circuit that I have worked on.
In the course of the alteration have you buried any cables in walls less than 50mm from the surface that need RCD protection ?
You don't need to provide RCD protection for parts of the circuit you haven't installed or altered.
Is supplementary bonding in place?
Does it need supplementary bonding? It's a WC, no bath or shower.
Thinking along the lines of taps on wash basin connecting to copper pipe of the installation.
No mention of light switch within the room could either be pull cord or wall switch which could be metallic.
The part of the installation you have ‘moved’ will need RCD protection. If it was a like for like replacement and you had not moved the light I would say no to installing RCD protection but I would comment on the MWC that it was missing.
Reply to Can anyone clear this up? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
nicebutdim
N
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks