Hello guys, Going to open a big can of worms here, but here goes. I'm having an argument with another electrician on site, and he is of the opinion that the is no regulation against the use of flex in domestic premises, for all circuits? I was always of the opinion that there was a regulation against the use of flex but I cannot seem to find one, in fact the opposite, when we looked and I cannot quote the exact reg now, but it says "as long as its suitable then its ok". I wondered if its something a simple a british standard marking, or is it literally due to the fact that twin and earth is a lot cheaper, nearly double the price for heat resistant flex, but surely you would recoup that in a couple of hours less work, due to the fact it would be easier to install. I also mentioned terminating it a the cutting of strands thus reducing surface area, but i suppose the reply to that would be "right tool for the right job" and your fine. Also perhaps T&E distinguishes a professional job from a DIY job... but hey ho. Tom
 
Last edited by a moderator:
Normal appliance cord flex, ...that i don't believe, especially if you were saying ''underfloor''!! As they would be at least using double sheathed cables. What was the marked type on the cable sheath??
 
Last edited by a moderator:
So it costs more, is physically bigger for same csa, heavier, harder to buy in bulk, takes longer to terminate, is the wrong shape for a lot of JBs, the strands are easier to damage, and needs more support.

OK. And still a debate about why it is not more common.

Someone normally says it can carry more current at this point ...
 
Normal appliance cord flex, ...that i don't believe, especially if you were saying ''underfloor''!! As they would be at least using double sheathed cables. What was the marked type on the cable sheath??

Im not saying it was appliance flex im saying it was multi strand flexable cable which was specified and ordered by the french main contractor
 
So it costs more, is physically bigger for same csa, heavier, harder to buy in bulk, takes longer to terminate, is the wrong shape for a lot of JBs, the strands are easier to damage, and needs more support.

OK. And still a debate about why it is not more common.

Someone normally says it can carry more current at this point ...

I agree with what you are saying, but there are still major pro's to consider. I mean its a lot easier to pull and run through joists e.t.c, it never kinks, and there are more and more tools coming on to the market that make stripping it as easy, if not faster to terminate than T&E, add to that you do not have to sleeve the earth, and it would make pushing the face plates on to back boxes a lot easier (given it isn't a big problem now).
 
Last edited by a moderator:
IMO it's ok to wire all circuits in flex provided they are terminated with a bootlace ferrule.
I don't think you'd save money on installation time though, taking the cost difference of materials into consideration.
You wouldn't be able to cable tie the cables to the central heating pipes because they're not part of the electrical system - if the customer wanted to rip out the central heating you'd be left with no support for the cables, so you'd pretty much have to install the cables the same way as with T&E, ie capped in plaster or clipped direct in the loft. Bear in mind that T&E lends itself better to being chased into walls due to it's flat profile.

Flex would make it easier to screw the faceplates back, but is that really worth the extra cost?
 
IMO it's ok to wire all circuits in flex provided they are terminated with a bootlace ferrule.
I don't think you'd save money on installation time though, taking the cost difference of materials into consideration.
You wouldn't be able to cable tie the cables to the central heating pipes because they're not part of the electrical system - if the customer wanted to rip out the central heating you'd be left with no support for the cables, so you'd pretty much have to install the cables the same way as with T&E, ie capped in plaster or clipped direct in the loft. Bear in mind that T&E lends itself better to being chased into walls due to it's flat profile.

Flex would make it easier to screw the faceplates back, but is that really worth the extra cost?

To be honest I've always used T&E and have never practically given it a go. I wonder if anyone has? If so does it justify the exra exspense? Also I usually chase the cables in pvc oval capping so i doubt the cable would make too much of a difference?
 
Last edited by a moderator:
521.9.3 - "A flexible cable or flexible cord shall be used for fixed wiring only where the relevant provisions of the Regulations are met" so there you go, clear as mud...
 
To be honest I've always used T&E and have never practically given it a go. I wonder if anyone has? If so does it justify the exra exspense? Also I usually chase the cables in pvc oval capping so i doubt the cable would make too much of a difference?
That's what I mean - oval capping is oval, the same as T&E, whereas flex is round. If you wanted to install round conduit in the wall you'd need to chase deeper, or use a larger (deeper) size of oval capping to get 2x flexes down side by side, but either way using flex would involve deeper chases.
 
one thing here though with flex boys.....dont forget that its CPC is insulated along its whole length and ideally you dont want that.....as an uninsulated CPC will intercept a fault before the fault goes L-L....ore line neutral....a short circuit.....so an RCD will operate as you are more likely to get an line-earth/neutral-earth fault......an important thing to consider on TT systems where an RCD is often the only means of fault protection likely do disconnect within times.....
 
one thing here though with flex boys.....dont forget that its CPC is insulated along its whole length and ideally you dont want that.....as an uninsulated CPC will intercept a fault before the fault goes L-L....ore line neutral....a short circuit.....so an RCD will operate as you are more likely to get an line-earth/neutral-earth fault......an important thing to consider on TT systems where an RCD is often the only means of fault protection likely do disconnect within times.....
The counter argument to this is that the CPC of flex is the same CSA as the live and neutral so it would have less impedance under a fault current and possibly faster RCD tripping times.

Please don't take this the wrong way, I'm not in favour of using flex instead of FT+e.
 
The counter argument to this is that the CPC of flex is the same CSA as the live and neutral so it would have less impedance under a fault current and possibly faster RCD tripping times.

Please don't take this the wrong way, I'm not in favour of using flex instead of FT+e.
the point i was making was that the CPC on a flex may not intercept the fault at all......yes ok..this can happen with T&E ....but less likely due to the structure of this type of cable....
 

Reply to Can circuits be hard wired in flexible cable? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top