Can i add new circuits onto installation with undersized main bonding? | on ElectriciansForums

Discuss Can i add new circuits onto installation with undersized main bonding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

goldie

Can i add new circuits to a system (rcd protected ofcourse) with under sized main protective bonding, without having to upgrade to 10mm2?
E.G tn-c-s earthing system with 6mm2 protective bonds but should be 10mm2 as neutral is less than 35mm2, This could be a code 4 on a pir or code 3 on a ecr which would not fail the inspection, but do i still have to make sure that the bonding is brought up to date?
 
My opinion, is that yes you can.
The requirement is to ensure the earthing and bonding arrangements are adequate (if required) for the safety of the protective measure you are going to install.
To my mind, bonding will not affect the operation of the RCD.
 
i assume you're talking of bonding to gas/water. if 6mm is adequate ( 50% of calculated minimum for main earthing conductor ) then it's OK.
 
i assume you're talking of bonding to gas/water. if 6mm is adequate ( 50% of calculated minimum for main earthing conductor ) then it's OK.
Exept where pme condition apply, It would then have to be 10mm2 if supply neutral is 35mm2 or less. Reg 544 i think? Dont think 6mm is adequate so want to make sure i dont carry out work until bonding is satisfactory, but also dont want to look asthough im ripping customer off by charging for un neccesary upgrade of bonding.
 
OK. measure your pefc. trhen use adiabatic to determine the min. size of main earthing for that pefc and the appropriate disconnection time of the DNO fuse. if that result is 12mm or less ( which it will be unless you have a very high pefc) then 6mm for bonding (50%) is adequate.
 
If I read it right, he's stated TN-C-S, therefore PME requires 10mm Protective Bonds if Neutral less than 35mmsq. Pg 134 Table 54.8 Reg 544.1.1
 
Yep makes sense to me, Thanks guys regs seem contradicting at times, Think i can jst about remember (I2 t)k etc??
 
Last edited by a moderator:
I'm not aiming to prove incorrect, I'd happily be told I am myself. Times on here I look at things & go away & find out myself, so this is one of them. Where's the Contradiction??? TN-C-S 16mm Earth, 10mm Bonds...Adiabatic is used on TN-S
 
If I read it right, he's stated TN-C-S, therefore PME requires 10mm Protective Bonds if Neutral less than 35mmsq. Pg 134 Table 54.8 Reg 544.1.1
so do i use my adiabatic equation or go with this regulation (this is why regs contradict in my opinion)
 
Goldie...Please don;t get me confused!!!! LOL...Adiabatic is for determining the Earthing Conductor by which Bonding conductors can be selected. Except...PME given by the Reg above...That's my take. Your 6mm is too low due to TN-C-S Earthing arrangement at current Regs. You can show the BRB Page info to your Client I guess...
 
Thanks claret. But am i allowed to commence work on this installation by adding circuit? see my first post then give me an answer please mate, so i can go to bed........... my head hurts
 
Yes where PME conditions apply, both the earthing conductor and the protective bonding conductors have to be a minimum of 10mm².
However, bonding is not required for ADS or for RCDs to operate, as such there is no requirement to upgrade the bonding.
 
Mate
I know how you feel!!!! My Head don't half hurt at times & fully agree the Regs are contradictory at best of times, but my opinion (& it's only that) is that I've given you correct info here. I don't do my own Notifiable work as I sub to Contractors but I'm sure it goes along the lines that prior to commencing you need to ascertain correct installation of Bonding Conductors - try the Part P doc? I'll take a look myself...Get some shut eye Mate...always time to look these things over. If you're scheme registered you can always run it by them too.
 
Yes where PME conditions apply, both the earthing conductor and the protective bonding conductors have to be a minimum of 10mm².
However, bonding is not required for ADS or for RCDs to operate, as such there is no requirement to upgrade the bonding.
understood but before i do certain works on an existing installation i have to make sure certain aspects of the installation is up to current standards i.e main protective bonding and mentioned rcds because any cable i install will have to be protected by rcd (unskilled persons and cables buried less than 50mm)
 

Reply to Can i add new circuits onto installation with undersized main bonding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
591

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top