Yes where PME conditions apply, both the earthing conductor and the protective bonding conductors have to be a minimum of 10mm².
However, bonding is not required for ADS or for RCDs to operate, as such there is no requirement to upgrade the bonding.
My point exactly wirepuller.You've lost me there spin.....the main bonding has nothing to do with ADS or RCD's...or am I missing something?..(been a long day).
Minimum 10mm is required on TNCS systems because the bond in theory may carry a significant load current under certain conditions...as long as the existing 6mm shows no signs of thermal damage it is reasonable to assume it is adequate, and there is no need to upgrade for a minor works which will not significantly change the characteristics of the installation. It would be good practice to upgrade,but in the end it is your call....you are the competant person.
Regulation 311.8
"No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of thedistributor, will be adequate for the altered circumstances. Furthermore, the earthing & bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate."
Is main protective bonding required for either ADS, or for an RCD to operate?
Supplementary bonding may be required for ADS, if circuit Zs are too high.
As such, if the protective measure you are intending to ues, does not require bonding to operate, there is no requirement to upgrade the bonding.
That's exactly what Spin is saying wirepullerYou've lost me there spin.....the main bonding has nothing to do with ADS or RCD's...or am I missing something?..(been a long day).
Minimum 10mm is required on TNCS systems because the bond in theory may carry a significant load current under certain conditions...as long as the existing 6mm shows no signs of thermal damage it is reasonable to assume it is adequate, and there is no need to upgrade for a minor works which will not significantly change the characteristics of the installation. It would be good practice to upgrade,but in the end it is your call....you are the competant person.
I get the replies guys from a Practicable view. IE: Do a Continuity check on the 6mm...Great! Visual check, Great! but without sounding a Jobsworth, the Regs don't do Practical Viewpoints. Only Black & White...& if this is interpretable for me I'd upgrade as then I've conformed...A PIR wasn't mentioned, only additional installations to current Regs...of which might be an EIC?...I think this'll be whatever each op is happy with...