During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms.

This could have been a coincidence, but I disconnected both neutrals from the neutral bar (i.e the kitchen lights and sockets) and tested between them. They showed continuity (0.97 ohms). Just FYI, there was no continuity with these neutrals to the neutrals of the other circuits.

This is a dual RCD board. K lights and sockets on the same side.

Does the fact the neutrals showed continuity mean this is a borrowed neutral? I have not come across continuity between neutrals before. Is this the correct test for them? Does it actually mean they are connected together somewhere, or am I missing other possibilities?

Also, as the neutrals have been connected together somewhere in the house between these 2 circuits, how do I find this join? The house is full of shoddy DIY alterations. I would like to offer at least a guess as to how you find this join, but for the life of me I cannot think of a way.
 
I'd say it's a fairly safe bet that with 0.98ohms between neutrals which have been disconnected from the neutral bar that you have a borrowed neutral.

I'd start by looking for any obvious DIY additions, like outside lighting or similar where someone could have picked up a live from a switch, not realising there is no neutral there and just run a neutral from the nearest socket.
You may find that this is also the location of the low IR fault.


You could disconnect a socket from the ring and split the ring into two halves. Test the neutral of each half to establish which half has the borrowed neutral connected.
Split that half of the ring again and repeat until you have narrowed down the location.
 
Is the IR still 0.10 with all neutral conductors for those circuits disconnected.
Yes. K lights removed (neutral) and sockets (neutral) removed from neutral bar. They then both test as 0.1Mohms to earth. Obviously both test the same as the N's have continuity. Liikely only one circuit actually has an IR fault, but I wont know until I find the join
 
Last edited:
I'd say it's a fairly safe bet that with 0.98ohms between neutrals which have been disconnected from the neutral bar that you have a borrowed neutral.

I'd start by looking for any obvious DIY additions, like outside lighting or similar where someone could have picked up a live from a switch, not realising there is no neutral there and just run a neutral from the nearest socket.
You may find that this is also the location of the low IR fault.


You could disconnect a socket from the ring and split the ring into two halves. Test the neutral of each half to establish which half has the borrowed neutral connected.
Split that half of the ring again and repeat until you have narrowed down the location.
In your example. If the line had been taken from a switch on the lighting circuit and the neutral from a nearby socket, how would that show continuity between neutrals? I realise there will be a resistance figure showing up between L and N as not all loads will be disconnected, but are there any appliances that would be as low as 0.97ohms? A halogen bulb for example would be around 90ohms. If there are such appliances then the culprit will be something as you suggest, otherwise the neutrals from both circuits are actually connected somewhere (I can't think of a reason why this would have happened though, meaning your example is far more likely, as long as it's possible to get such a low reading between L and N).

The fault finding is exactly the same as for an IR fault! Of course, simple, thankyou. Yes, I may well find the IR fault in the same location, at least hopefully I will.
 
First place I’d look would be the two way lighting for the stairs, if you have them. Any dodgy wiring in and around kitchen cabinets etc?
 
First place I’d look would be the two way lighting for the stairs, if you have them. Any dodgy wiring in and around kitchen cabinets etc?
2 way lighting seems to come up alot with borrowed neutral when reading other threads, but this is with the sockets. Kitchen cabinets certainly worth a look as it's all DIY.
 
With a long lead (resistance calibrated out) you could measure from the lighting N to he N at various sockets on the socket circuit. The resistance will decrease as you get closer to the point of interconnection (I'm assuming only one point, as more than one will complicate things). You could also repeat the other way round, and find the lighting point closest to the point of interconnection.

NB: disconnect the N of both circuits from the N bar first!
 
With a long lead (resistance calibrated out) you could measure from the lighting N to he N at various sockets on the socket circuit. The resistance will decrease as you get closer to the point of interconnection (I'm assuming only one point, as more than one will complicate things). You could also repeat the other way round, and find the lighting point closest to the point of interconnection.

NB: disconnect the N of both circuits from the N bar first!
Interesting idea. I guess you would need to have an idea of the layout though. It could help with an indication of the area though, as you say.
 
What does everyone think about the actual figure of 0.97ohms? Could this be a borrowed neutral (In which case the figure 0.97 ohms must be going through the load somewhere) or with a figure that low does it have to be 2 neutrals actually connected?
 
From your description, I'd say neutrals are directly connected together somewhere. IME not many loads have very low continuity across them like that (I think perhaps a compressor might be one example).

If they were connected through a load, it would likely have to be through 2 loads. Eg N1 - load1 - L - load2 - N2. But then you're measuring continuity across 2 loads, unlikely to be very low.

Or if N1 - load - N2, then the load wouldn't work as no potential difference across it. Again, unlikely.
 
Would seem to be directly connection somewhere

An interesting one I had a few years ago, the L&N from a PIR on a socket circuit was connected to a L&N from a light circuit at an outdoor light. Intent was the light switch overrode the PIR when required. The N was always interconnected, while the L connections only got interconnected when the PIR operated and the light switch was on at the same time!
 
Well this is looking like an odd one then.

What possible reason could there be for an actual neutral connection between lights and sockets! I suppose the DIY homeowner could have just got confused with a few junction box and put all the black conductors together.

I shall update when I find it.
 

Reply to Can I confirm how to test for and how to find a borrowed neutral? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
Thanks very much for your help chaps. It turned out to be reversed polarity and some dodgy DIY stuff. I'll go back another day to sort it...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top