There is a double socket on the wall where the main feed comes in and this is then connected to a none switch fused socket. Iv'e been told i can add a other fused switched socket and connect both together then run 2 additional sockets off the fused switch one?
Welcome to the forum mate.
What do you mean by a "none switched fused socket"? Do you mean one of these?
Does the circuit you are adding to have RCD protection?
Does the way you intend to add the extra sockets need the wires to have RCD protection?
We need more info mate.
I'm looking again at the original question.
why would you want to add another fused connection after the first?
so:
ring socket <---xFCUx---xSKTx---xSKTx
if those sockets take more than the first 13A fuse they will stop (fuse blows).
so:
ring socket <---xFCUx---xSKTx---xSKTx--xFCUx---xSKTx
makes no sense - the same would happen. The first FCU protects the connected sockets.
That said. You need to look at what loads you are expecting to connect and where they are positioned on the ring. By design a leg on the ring (the cable between sockets) the Iz shouldn't go above 20A. If you are adding these sockets to either end of the ring, those closest to the CU - you could well do that. You need to calculate the leg length impedances for the final ring and calculate the expected current going both ways (parallel circuit). Someone qualified and with the correct test equipment can calculate these for you to make sure this would comply.
He posted at 4:56 am. Maybe posted before work or after night shift? So either he's just due home or just getting up?? I didn't even realise that time existed on a Sunday.
Reply to Can i connect 2 sockets to a fused socket and this inturn to a other fused socket in the Electricians Jobs area at ElectriciansForums.net
Electricians Jobs, Electricians Mate Jobs and Electrician Apprenticeships
Thanks for visiting ElectriciansForums.net, the worlds largest electrical and electricians community. This area of the website is for those who are looking for electricians jobs, electricians mate jobs, or electrical apprenticeship schemes.
We have opened up our website to the world after being UK-only for more than 10 years. We now have jobs posted to the forum for domestic, industrial and commercial electrical work from all over the world.
Anybody is welcome to register to our forum for free. You can post jobs you have going, or know of. And you can also post to the forum if you're looking for employment or recruitment. Full or part time. Just let us know the full details of the job you have on offer or are looking for and we'll do the rest.
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc