Somecamel

Hi,

Run into a strange problem today, could be something simple but for the life of me couldn't work it out.

Finished off fitting a 2.45kW PV job today, electrician came last Saturday to do the AC connection etc. (CU is being changed this weekend as not in regs)

It's 10 Canadian 245 with a Power One Uno 2.5 (2 strings of 5)

All connected up to inverter but inverter wouldn't kick in. (LED backlight came on but thats all, no data on screen) Tried another Uno I had in the van and again same problem.

Popped a steca 3.6 on to see if it was the powerone's (same batch) but no AC voltage was coming through.

Checked AC isolator and showed 247v coming in so somewhere between the AC isolator and the inverter (had bypassed the Gen meter to test) it cant get the grid voltage.

Could it be the old CU? I cant work out how I can get 247 from the isolator but the 3 inverters I tried it with don't see it.
 
Did you check for 247 on the inverter terminals?

You know what I can't remember :( I'm sure I must have done, if I didn't could be a dodgy Isolator maybe, it's been one of them days :P

Edit:- The inverter did power up though so maybe I didn't
 
Thats what it sounds like to me - 247 "in the iso" but not 247 "out of iso" so maybe? :-)

- - - Updated - - -

Tell you what ive had in the past - wires appear clamped in the iso - when in fact they are tucked behind the clamp, easy to do on some of them.
 
I'd expect it's a start up voltage issue as the standard start up voltage is 200V.

You can reduce the start up voltage down to 120, but you'd be much better running it in a single string of 10 panels, as this is far closer to the peak efficiency point on the voltage curve.
 
I'd expect it's a start up voltage issue as the standard start up voltage is 200V.

You can reduce the start up voltage down to 120, but you'd be much better running it in a single string of 10 panels, as this is far closer to the peak efficiency point on the voltage curve.


But surely the inverter should have the info on the LCD display? there was nothing on the PO Uno display
 
oh, well then it sounds like you've got a faulty ac isolator or something, and just need to trouble shoot the AC circuit to find the fault.

but then when you've done that you'd still be a lot better off running it as a single string IMO.
 
But surely the inverter should have the info on the LCD display? there was nothing on the PO Uno display
if you've got a combination of no AC, and DC under voltage then it probably won't fire up at all.

Which sounds like what you've got going on... have you been walking under ladders / smashing mirrors recently?
 
Fair do's, put them in 2 strings due to shading, they're the CS5P-245M

- - - Updated - - -

if you've got a combination of no AC, and DC under voltage then it probably won't fire up at all.

Which sounds like what you've got going on... have you been walking under ladders / smashing mirrors recently?


No I started a solar company a few years ago :P Im doomed
 
I just checked also as i started to doubt myself :-P 2 x parallel is spot on according to the PO sizing tool - i would say AC Iso.
 
To be fair, I don't think the voltage went above 173v today (when tested)- crappy weather, so could be this.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Can I pick your brains?
Prefix
N/A
Forum
Green Lounge (Access Only)
Start date
Last reply date
Replies
16

Thread Tags

Advert

Thread statistics

Created
Somecamel,
Last reply from
solarsavings,
Replies
16
Views
193

Advert

Back
Top