Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was an 8.5kw, I would like to install a 9.5kw... the cable to the shower is 10mm, it is only around four meters from the consumer unit, and the 10mm cable runs through the small loft space and on top of any insulation. Currently there is a 40a mcb for the shower circuit in the consumer unit... and this is where my question lies. According to instructions I have downloaded from various showers they all seem to state: 9.5kw shower requires a 40/45a breaker. When doing the calculation (9500 / 230 = 41.3) clearly that is over the 40a that is currently there. Would the 40a be sufficient in this case and would a 50a (they dont do a 45 for my consumer unit) be 'too' big and potentially dangerous..?
Many Thanks in advance for any info.
 
Assuming there is also 30ma RCD protection in place for this circuit and the cable run is exactly as described I'd upgrade the MCB to a 50a if 45a isn't available. it's a bad idea for any overcurrent device to run at a slight overload constantly and although it probably wouldn't 'trip' an upgrade is much better.
 
Assuming there is also 30ma RCD protection in place for this circuit and the cable run is exactly as described I'd upgrade the MCB to a 50a if 45a isn't available. it's a bad idea for any overcurrent device to run at a slight overload constantly and although it probably wouldn't 'trip' an upgrade is much better.
Ok, thanks Dave.
 

Reply to Can I simply change this over. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
997
  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
936

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top