I have a Crabtree Type SB6000 CU. It has a spare way with a redundant MCB Type 1 6A. I was hoping to use it for a small lighting circuit. Can someone of more experience than myself advise me if the Type 1 MCB could be used under BS7671 17th edition?
 
Yes, you can use an existing BS3871 Type 1 MCB (2.7 to 4 In trip current in the conventional time 0.1 to 5s), which is roughly equivalent to BS EN 60898 Type B MCB (3 to 5 In). These older devices should not be specified for new installations, hence the reason they were removed from BS7671 over 10 years ago.
 
Yes, you can use an existing BS3871 Type 1 MCB (2.7 to 4 In trip current in the conventional time 0.1 to 5s), which is roughly equivalent to BS EN 60898 Type B MCB (3 to 5 In). These older devices should not be specified for new installations, hence the reason they were removed from BS7671 over 10 years ago.

Thanks for this informative response. To help me still further why can they not be specified for new installations? And does this reason not also apply to a new circuit added to a current installation?
 
they are not used anymore because we have progressed. same as cars don't have x ply tyres or rod brakes anymore. but by the same token you can add a new circuit to an existing installation if that circuit complies with disconnection times. only thing would be if the lighting circuit were in a special location , it would require RCD protection.
 

Reply to Can I use Type 1 MCB in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

If the main DB RCBO is there to provide additional protection (as it most probably is), then no, as S type RCDs are not suitable for providing...
Replies
1
Views
1K
loz2754
L
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top