Thanks for responses, been away today hence no reply sooner. So yep the rotary isolator as mentioned is just above and fed from the CU mcb, so that would be the AC to inverter isolator. So if this was switched off then would/could the solar system still cause an earth fault to flow ? and yes its a split load board, not my install. Is it likely that a fault to earth could manifest via the panels or inverter (when the inverter feed is isolated) and find its way through the cpc feed back to the CU ?, or through any bonding of the solar system ? Do solar systems even have bonding ??? As I said im not familiar with solar.
Im not sure it is the solar causing this issue, the story goes thus:
I took a look at this when (customer - friend of a friend) reported nuisance tripping, the RCD in question tests fine on ramp test (19mA or so) and is feeding 4 or 5 circuits, one of which is the solar. Before removing the CU cover to look at the circuits I isolated the solar at the rotary isolator above the CU. with all appliances disconnected from the x2 rings on this side of the CU and all the lights on, my clamp meter was not picking up anything obvious from the cpc's of these circuits (clamp meter is a bit el cheapo thou). IR testing of these circuits was good aswell. However, one of the ring circuits was causing a trip when carrying out a 3 lead low loop test with all other circuits switched off. Switched off the boiler at the spur and loop test caused no trip, strange thing is my clamp meter was picking up no stray current to earth while the boiler was powered up via the rings cpc or any bonding. So, I said its likely your boiler has an earth fault that's intermittently tripping the RCD as earth leakage is accumulating with any other earth leakage from equipment and tipping it over the RCD's 19mA. I suggested getting all the equipment pat tested and your boiler looked at before doing anything else.
Since then and now customer has told me that her neighbours on her estate have experienced a similar tripping issue, and it seems that the solar panels have been causing it. Hence my original question. As the solar was isolated when I carried out the offending loop test assumed that it could not be a contributing factor; but thinking more the solar is always generating something isn't it , even when its isolated, so my question again, can there be leakage to earth from a solar panel array thats isolated on the AC side ??
Thanks in advance