Is kva not simply kilowatts?
If a pure resistive circuit then yes otherwise no
If you and the missus were at it
When you thrust,the missus does the same at the same time,result,bliss (good power factor)
If you and the girl next door were at it
When you thrust, she is little bit faster than yours,result,out of sinc ( possible dis conection even) (poor power factor)
Power factor is trying to achieve unity ( 1 to 1 ) It may be only 0.8 or so or worse even)
volt x amps (x power factor) = true power
So the better the power factor the more the unchanging volt amps value matches the true power
Correct mate, i do have one of these forms to fill in. So i have a load of 83kw so i devide or multiply this by 0.8 to get my kva? Its a 3 phase supply i need so do i devide the 83kw by 230 or 415 to get my ampage? Cheers in advance.Sounds like someone might have got one of those forms to fill in for a new or increased electricity supply, as these ask for amongst other things, how many kVA do you require. I always put 21kVA as this ensures that a 100amp fuse is fitted. Anything above about 25 kVA puts you onto 3 phase.
I'm a bit too long in the tooth for serious maths, and i've forgot most of the formulaes i sort of learnt 30 odd years ago. I'll stick with V over IR etc etc.
Cheers........Howard
Where does the 1.73 come from mate?Correct mate, i do have one of these forms to fill in. So i have a load of 83kw so i devide or multiply this by 0.8 to get my kva? Its a 3 phase supply i need so do i devide the 83kw by 230 or 415 to get my ampage? Cheers in advance.
(83kW x 1000) / (230 x 1.73 x 0.8) = Amps