Just been to a subdivided house - now up+downstairs flats. There are two earth rods which go to a single earth block under the floor, then leave the block as two earths up to the C/Us. (Effectively each flat is connected to the two spikes). There is a single mains head with 100A BS1361 fuse which then loops up to another single 100A main fuse (for one flat) and then loops on to another such fuse for the other flat (DNO fitted).

Question: can this supply be converted to PME?
Issues: can a single earthing conductor feed two separate dwellings? I've got distant voices saying in my head that this isn't allowed.

Thanks for any advice.
 
Sounds like you have 3 x 100A fuses in series.

I would say that's a bit of a no no, as there's no discrimination.

Or have I misunderstood :confused:
 
Last edited by a moderator:
sounds like they have looped off the live side of the fuse,so its in paralell. im not sure whether you are allowed to share rods, but im guessing that if you were, then seperate conductors would be needed.
 
I don't think it's three in series, as it goes through the first fuse then to the second - but is looped to the third from the supply/feed side of the second fuse, not from the load side. But even this means there's two 100A fuses in series for each flat.

And it would be a question of whether the shared (first) fuse blew before or after the individual fuses, in an overload situation. So there's the real possibility that an overcurrent/overload on one dwelling affecting the supply to the other. Cheers JUD.
 
Ah, replied at the same time as you johnboy.

Yep, that's the setup. I'd like to just get rid of the whole mess under the floor and PME it. But due to the shared incomer, the PMEd main earthing conductor would be shared up to a block, where it would be split for each flat. I'm sure I've read somewhere that this isn't allowed, but can't find anything about it anywhere. Or is this a figment of my imagination?!
 
You may have read the many threads about not exporting PME to outbuildings.

Never been in your situation, but I found a similar thread on IET forum that may be of help.

IET Forums - Advice needed on EDF TNCS supply
 
I would have thought that as there is a single head feeding both flats that is classed as one source of supply therefore a TNCS earth from that source of supply can serve an MET at the intake with a main earth to each flat.
 
sounds like they have looped off the live side of the fuse,so its in paralell....

It's just occurred to me, would this be allowed as there would be no overcurrent protection for the cables that are looped off.
 
Last edited by a moderator:
yeah its protected by the suppliers cut out. its the same as your tails in a normal cu. you can t off them in a henley block. this is effectively the same thing.

Which brings me back to my first post. As it's feeding another 100A fuse it is wired in series (not parallel) and there is no discrimination between the 2. If the downstream fuse was 60 or 80A then there wouldn't be a problem.

Normally when you split the tails in a Henley block you are feeding other DBs and not a second 100A fuse.

Are you with me?
 
Last edited by a moderator:
lets say that you have a cable running from a to b, rated at 200a. you then want to tap off that at various points, to houses. you would joint the cable and t off at these points with whatever size cable needed for the load. at the nearest convenient point, you would supply protection to that cable (suppliers cut out).

each of those tap offs are in pararell with the others.

if you had the same set up, but above ground, then do away with the joints, and loop the cable at the cut outs, and that is what it seems like has happened at thes post. the original 200a cable is protected elsewhere( at the sub, or lucy pillar ect)
 
If a 100A fuse is protecting a cable that is feeding another 100A fuse then it is wired in series and there is no discrimination between the 2 fuses.

If a 100A fuse is protecting a cable that is feeding a 60 or 80 fuse then it is wired in series, but this time the 60/80A fuse provides discrimination.
 
Thanks for your interest chaps. Here's a couple of pix i took. The first is the shared mains head. The second shows how the live split, looped on and protected by the fuses. And you can see the neutral split in the adjacent Henley block.

Thanks JUD for the IET forum posting. I'm still going over it.....

I suppose one fact here about sharing the PME earth conductor is that both dwellings have full access to it as it's in the shared entrance hall. So there are no issues about access and safety.
 

Attachments

  • [ElectriciansForums.net] Can Two Dwellings (Upstairs+Downstairs flat) Share PME Main Earth?
    IMAG0178.jpg
    181.5 KB · Views: 50
  • [ElectriciansForums.net] Can Two Dwellings (Upstairs+Downstairs flat) Share PME Main Earth?
    IMAG0177.jpg
    76.8 KB · Views: 44

Reply to Can Two Dwellings (Upstairs+Downstairs flat) Share PME Main Earth? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

462 excerpt below. The incoming supply is via a electrical plant room to the block of flat, each flat has a standard DNO cutout fuse but no...
Replies
9
Views
1K
  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top