I think the course I was on ( 3yrs @ 1 day a week ) was symptomatic of the way this country has gone in the last few years, "keep it simple & go heavy on the Health & safety". I have lots of questions to ask which most of you will roll your eyes at.

Don't be afraid Jonny to come on and ask questions son, the majority on here are more than willing to try and fill gaps left in your training.

as I said in my post to you, it's not your fault that your trained in this way, and a few of us older lags would have trained you properly, or at least shouted at you properly.............:D
 
s = i sauared x time, square rooted and divided by k

example 20A type b

100x100x0.4 =4000 square rooted = 63.2 divided by 51(k value) from table 54.4= 1.2mm swa core you need as minimum....
 
I know mate I sometimes just can't believe what is happening to our industry.

Not this young lads fault but the institution.

Apparently teaching someone to run a cat cable and terminating a RJ45 plug is considered more relevant to an electrician than running and terminating MICC.

Malcolm,

It even seems that these so-called lecturers are teaching students to favour radial circuits over RFCs !!! It's not going to be long, if that continues, that the sparks of tomorrow will be gasping in despair at the thought of having to fault find a ring circuit let alone test one!!

I think the whole curriculum of student training, needs a good kick up the arse. Just wait and see all the lecturers on here now, come back defending all the modern virtues of the courses they run ... The fact is, at best all we are producing these days are poorly trained domestic installers. It's left to them, to gain the experience they need, to become a well rounded electrician
 
Malcolm,

It even seems that these so-called lecturers are teaching students to favour radial circuits over RFCs !!! It's not going to be long, if that continues, that the sparks of tomorrow will be gasping in despair at the thought of having to fault find a ring circuit let alone test one!!

I think the whole curriculum of student training, needs a good kick up the arse. Just wait and see all the lecturers on here now, come back defending all the modern virtues of the courses they run ... The fact is, at best all we are producing these days are poorly trained domestic installers. It's left to them, to gain the experience they need, to become a well rounded electrician

I think mate that is another of those nails hit firmly on the head there.

I have to say working overseas for a number of years I have gotten out of the RFC way of thinking, but I personally feel that in many cases it is a viable and a best option.

As you say the trouble with RFC is that it is much more complicated when designing it and testing it, than a bog standard radial. The rule of thumb methods of finding the cable Iz by multiplying the protection device by 0.67, working out Volt Drop and loading the ring, will as you say be a thing of the past, much the same way as MICC is.

I suspect your right tutors/training centres will say it is "development" and "modernizing" of the industry and I suppose it is, but for me still a shame.
 
Nothing to do with the IET, but it has everything to do with the lecturers and promoting their own prejudices especially when they are factually and/or fundamentally Wrong!!

We have one lecturer here, that has openly stated that he guides his students away from RFC when providing socket circuits!!! Probably also tells them they can't use a SWA armouring as a CPC too... If these so-called lecturers can't be constructive in the advice they give to there students, then best keep their ill founded opinions to themselves and not burden the students to perpetuate them
 
I kind of skipped pages 2-12 but if all this hype about using a seperate earth is becoming so much more common, why would buying 5 core SWA not become more common instead of running a seperate earth?
 
I recently found an swa used in this way to a garage, personally in such a zone I would never try to use the sheathing and so installed a rod to earth the satellite box, maybe I dont like to cut corners but then I never take chances just for an easy life
 
I recently found an swa used in this way to a garage, personally in such a zone I would never try to use the sheathing and so installed a rod to earth the satellite box, maybe I dont like to cut corners but then I never take chances just for an easy life

So you think a rod is better than a TN system earth do you?? .....Then your a fool !!!
The mind just has to boggle at some of the completly daft an ill informed statements such
as this one.
 
I recently found an swa used in this way to a garage, personally in such a zone I would never try to use the sheathing and so installed a rod to earth the satellite box, maybe I dont like to cut corners but then I never take chances just for an easy life


Perhaps you'd care to elaborate on what corners are being cut & what chances are being taken by using the knowledge we glean over the years coupled with the training we received, to establish the suitability of a particular material for a particular application???

Not doing something because you 'dont like it' (or dont know any better), then claiming those that do are 'cutting corners' & 'taking chances' is nonsense frankly.

You'll also have to enlighten me on how an Ra of 100-200ohms (probably), is better than a Zs of around 0.5-0.7ohms......
 
In respect to the above posts,, I never take the earth from a property out to an external area, garage shed etc. even though as you say a good Zs from a TN system is a lot better than a high Zs on a TT.. the taking of one earth potential ( the house) to an external area such as the garage can cause (and I have seen it) a potential diffrence..

my main aim when wireing to out buildings is keeping any fault current/ voltage below 50v and appropreate disconection times. Ive seen lost neutrals on PME systems where outhouse neutrals and earths have become live to the surounding earth... would hate to step out that hot tub bare foot onto tera firma.. but hey thats me.. and I know this argument has been done to death, but ive seen the consequences of taking earths from diffrent areas and felt the potential diffrence!!!! :rolleyes4:

im not starting an argument... its just what i feel,, and as long as we are safe and follow the regs,, then we all win!!
 
Last edited by a moderator:
Well, this is where the training & experience I mentioned earlier comes into play!!!

yep too right,, but too date,, with my training and experience, ive never been able to predict the failing of a neutral on a pme system,, if i could i would be doing other things .. "joking please dont rip into me":)
 
Last edited by a moderator:
I never 'rip in' to anyone.:15:


I just get a bit wobbly when a blanket statement is made on a topic & the only reason being that someone doesn't like doing it the other way.


Obviously there are a number of situations where certain methods of doing things aren't appropriate, but to tar all with the same brush without any thought is a bit blind IMO.

This is almost turning into an extending pme thread (:wacko:), we best leave it there I think.:)
 

Reply to Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
420
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
yes it was a pee-take... I was commenting if someone was dumb enough to use earth clamps on armour, they might just be dumb enough to earth a...
Replies
6
Views
513

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top