Can you add additional sockets to non RCD protected circuits via RCD spurs or sockets? | on ElectriciansForums
Discuss Can you add additional sockets to non RCD protected circuits via RCD spurs or sockets? in the UK Electrical Forum area at ElectriciansForums.net
Leicester
Evening all,
If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or fitting RCBOs, is it permitted to add additional sockets to the circuit via RCD spurs or additional RCD socket outlets? (type A of course)...if the sockets are not installed its likely excessive amounts of extension leads will be used and items would never have any additional protection. In my eyes it is only making the situation safer and if the customer wont upgrade and replace a consumer unit, what is the alternative?
The alternative is walk away from that job.
The rcd doesn’t just protect the user of a faulty appliance being plugged in, but the cables within a circuit from accidental damage.
You haven’t mentioned how it’s wired, but I’ll guess at t&e buried in plaster.
Is the CU so old that you can’t get RCBOs to fit?
Evening all,
If adding a socket circuit, then I can't see why a rcbo couldn't be used at the Cu.
Adding circuits is going to be notifiable.
The short answer is yes.
If the RCD is only needed for additional protection to the socket outlets, and isn't needed to protect cables buried in walls, meet disconnection times, etc etc, then it is ok to use RCD spurs or sockets to protect the outlets.
Agree So long as the new cable isn't chased into a wall I see no real issue with RCD sockets
Cant see why they don't just fit a rcbo would be cheaper than buying a rcd socket.
What about fitting the spd....
And the testing, of course.
Cant see why they don't just fit a rcbo at CU would be far safer and cheaper than buying a rcd socket.
A bit more context the boards are Bill from memory so probably 1970s RCBOs do not fit within the consumer unit as they didnt exist when the board where made and there isnt space for an RCD enclosure in the surrounding areas (its an old care home fuse board)... The cables supplying the new sockets would be in YT2 trunking. I know its not ideal and a board change is best but the fact is that wont happen and surely an additional RCD protected socket or two is safer than using trailing extension leads used on the exisiting non protected sockets
Ahh, makes sense now.
No room for a single rcbo enclosure ??
Yes, I agree better with than without.
It's not still a care home is it?
I would have thought a care home would have had to have kept up with safety standards
When I've carried out inspections on them in the past I would have to say that that's not my experience of them. I'd well believe the old Bill rewireable fuse boxes being there.
Reply to Can you add additional sockets to non RCD protected circuits via RCD spurs or sockets? in the UK Electrical Forum area at ElectriciansForums.net
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
nicebutdim
N
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...