Evening all,

If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or fitting RCBOs, is it permitted to add additional sockets to the circuit via RCD spurs or additional RCD socket outlets? (type A of course)...if the sockets are not installed its likely excessive amounts of extension leads will be used and items would never have any additional protection. In my eyes it is only making the situation safer and if the customer wont upgrade and replace a consumer unit, what is the alternative?
 
The alternative is walk away from that job.

The rcd doesn’t just protect the user of a faulty appliance being plugged in, but the cables within a circuit from accidental damage.
You haven’t mentioned how it’s wired, but I’ll guess at t&e buried in plaster.

Is the CU so old that you can’t get RCBOs to fit?
 
Evening all,

If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or fitting RCBOs, is it permitted to add additional sockets to the circuit via RCD spurs or additional RCD socket outlets? (type A of course)...if the sockets are not installed its likely excessive amounts of extension leads will be used and items would never have any additional protection. In my eyes it is only making the situation safer and if the customer wont upgrade and replace a consumer unit, what is the alternative?

If adding a socket circuit, then I can't see why a rcbo couldn't be used at the Cu.

Adding circuits is going to be notifiable.
 
The short answer is yes.

If the RCD is only needed for additional protection to the socket outlets, and isn't needed to protect cables buried in walls, meet disconnection times, etc etc, then it is ok to use RCD spurs or sockets to protect the outlets.
Agree So long as the new cable isn't chased into a wall I see no real issue with RCD sockets
 
Cant see why they don't just fit a rcbo would be cheaper than buying a rcd socket.
What about fitting the spd....
And the testing, of course.
Cant see why they don't just fit a rcbo at CU would be far safer and cheaper than buying a rcd socket.
 
A bit more context the boards are Bill from memory so probably 1970s RCBOs do not fit within the consumer unit as they didnt exist when the board where made and there isnt space for an RCD enclosure in the surrounding areas (its an old care home fuse board)... The cables supplying the new sockets would be in YT2 trunking. I know its not ideal and a board change is best but the fact is that wont happen and surely an additional RCD protected socket or two is safer than using trailing extension leads used on the exisiting non protected sockets
 
A bit more context the boards are Bill from memory so probably 1970s RCBOs do not fit within the consumer unit as they didnt exist when the board where made and there isnt space for an RCD enclosure in the surrounding areas (its an old care home fuse board)... The cables supplying the new sockets would be in YT2 trunking. I know its not ideal and a board change is best but the fact is that wont happen and surely an additional RCD protected socket or two is safer than using trailing extension leads used on the exisiting non protected sockets


Ahh, makes sense now.

No room for a single rcbo enclosure ??

Yes, I agree better with than without.
 
Last edited:
A bit more context the boards are Bill from memory so probably 1970s RCBOs do not fit within the consumer unit as they didnt exist when the board where made and there isnt space for an RCD enclosure in the surrounding areas (its an old care home fuse board)... The cables supplying the new sockets would be in YT2 trunking. I know its not ideal and a board change is best but the fact is that wont happen and surely an additional RCD protected socket or two is safer than using trailing extension leads used on the exisiting non protected sockets


It's not still a care home is it?
 
I would have thought a care home would have had to have kept up with safety standards
When I've carried out inspections on them in the past I would have to say that that's not my experience of them. I'd well believe the old Bill rewireable fuse boxes being there.
 

Reply to Can you add additional sockets to non RCD protected circuits via RCD spurs or sockets? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
455
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top