out of interest, what if the supply is Protective neutral bond?

Still TN-C-S but not PME!

Thanks.
From my point of view, even though I have not seen this referenced, the purpose of increasing the size of the earthing conductor on a PME system is because the earthing conductor may, in the case of the loss of the external supply neutral, carry the installation load current via the extraneous conductive parts.
In the case of a PNB system the earthing conductor will not carry the installation current if the supply neutral is lost as there is no circuit from the earthing conductor to the transformer star point. Also because of the more limited nature of the neutral conductor there is a lower chance of disconnection even if there happens to be a casual earth path of high resistance. Therefore I believe there is no requirement to apply the increased csa requirements needed where there is a PME supply.
 

Reply to Can you join Main Protective bonding conductor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
822

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top