I've been asked to provide and install a garage supply which will have sockets and lighting to run off.
The house is on an TT System i'm getting an ze of around 9MOhms, all socket circuits are 16a all circuits have rcd protection. Getting back to the Consumer unit for a new supply is going to be a nightmare. So i'd like to avoid doing this as the owner doesn't want surface trunking in the house or her bedroom carpet lifted which is only 2 weeks old! add to this the upstairs floors are all different levels and i can see issues getting through parts.
I have 2 radial circuits i could use that are approx 2/3 meters away from the garage each have around 7/8 sockets on them.
Can you see any issue with upgrading the mcb for one of these radials to 20a providing all cables are run in a way to allow for an 20a breaker which i'm sure i'll be fine to do at this point.
and extend from the end of line to a DP Switch so all power can be isolated from within the house and from there go into an adaptable box in 2.5mm TE. and from the adaptable box run some 4mm 3 core swa into the garage into an 2gang garage consumer unit. Is it okay to rely on the exsisting stake or should i install a new one for the garage and finnishing the cpc at the garage end on the swa
The breaker sizes within the garage consumer unit will be 16a and 6a both covered by an 30ma rcd
The house is on an TT System i'm getting an ze of around 9MOhms, all socket circuits are 16a all circuits have rcd protection. Getting back to the Consumer unit for a new supply is going to be a nightmare. So i'd like to avoid doing this as the owner doesn't want surface trunking in the house or her bedroom carpet lifted which is only 2 weeks old! add to this the upstairs floors are all different levels and i can see issues getting through parts.
I have 2 radial circuits i could use that are approx 2/3 meters away from the garage each have around 7/8 sockets on them.
Can you see any issue with upgrading the mcb for one of these radials to 20a providing all cables are run in a way to allow for an 20a breaker which i'm sure i'll be fine to do at this point.
and extend from the end of line to a DP Switch so all power can be isolated from within the house and from there go into an adaptable box in 2.5mm TE. and from the adaptable box run some 4mm 3 core swa into the garage into an 2gang garage consumer unit. Is it okay to rely on the exsisting stake or should i install a new one for the garage and finnishing the cpc at the garage end on the swa
The breaker sizes within the garage consumer unit will be 16a and 6a both covered by an 30ma rcd