Hi,
We have just finished a building which contains 10 of Compact Flourescent 2 x 18w PL downlights with gear. When connecting a normal white rocker switch the lights operate fine, however when using the 2 gang electrical touch switch the lights do not seem to work. Any idea to why this is and how i can resolve this problem?

Here is the spec for the light switch:

[h=5]TECHNICAL SPECIFICATION:[/h]
  • [h=5]Rated Voltage: 220~240V AC, Frequency: 50/60Hz[/h]
  • [h=5]Capability allowance: -15%~+10% 187~264V[/h]
  • [h=5]Operating Power: 2 Gang (15-1500W),[/h]
  • [h=5]Working Environment: Working Temperature: 0[SUP]o[/SUP]C~40[SUP]o[/SUP]C Relative Humidity: 10% - 93%[/h]
  • [h=5]Energy Consumption: <0.02W[/h]
  • [h=5]Measurement: 86x86mm[/h]
  • [h=5]life: 100,000 times at least (relay useful life) Remote usage distance >20M[/h]
  • [h=5]Power: < 0.1mW[/h]
  • [h=5]CE & RoHS Certified[/h]
Many Thanks In Advance,
Ash
 
Re: Cannot get electrical light switch to turn on commercial PL Downlights, Please he

anything with a 240v coil and contacts rated higher than the load current.
 
Re: Cannot get electrical light switch to turn on commercial PL Downlights, Please he

Use Google to locate a suitable relay. There’s 1000’s to choose from, I’m not trawling through then for you.

I’m sorry but you took the job on without knowing what you were doing. It’s a commercial job so I would assume you have some experience of the trade.
 
Re: Cannot get electrical light switch to turn on commercial PL Downlights, Please he

I would tend to agree with Trev and ensure that you have the correct connections, from the wiring diagrams for the touch switch the terminal identification is apparently the same as you would expect for a two way switch but the function is different.

If you are using a two gang touch switch are you also using a two gang rocker switch?
A two gang rocker switch with a permanent line looped to the commons and individual switched lines one coming from each of the L1s should then be wired on the touch switch with the permanent line to L and the switched lines individually to L1 and L2 respectively.

Using a single gang rocker switch and connecting permanent line to com and switched line to L1 and it is working; then connecting the touch switch permanent line to L and switched line to L1 and allowing 2 minutes after power up before testing then it should work, however you would only be using one of the two gangs on the touch switch.
 
Re: Cannot get electrical light switch to turn on commercial PL Downlights, Please he

As already said in earlier posts,

The touch switch is only designed for resistive loads and not suitable for inductive loads such as the PL lamps and their ballasts.

The OP needs to choose the correct type of controls as even with a contactor/Relay you end up with inductive load for the touch switch. Then there is the minimum 'holding current' for the triac, which means that load must be large enough, other wise the Triac will not conduct, as the minimum current required for the Triac to conduct will not flow.
 

Reply to Cannot get electrical light switch to turn on commercial PL Downlights, Please help. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top