Hi, I cant get a Zs reading from the majority of my new circuits. I do get a reading between the incomers to the d.b and the main earthing conductor and I can get the RCD tripping. The system is TT and its a total rewire. Any help would be appreciated.

Go back to the beginning. You get a Ze reading between incommers and main earth. I presume this is using the normal Ze measurement. Can you get a Ze measurement between incommers and main earth using the RCD function?

If the answer is No then you have a meter problem. (The only difference is the way your meter is measuring Ze; one way it works, one way it dosn't). Solution: use a calculation for Zs [= Ze + (R1 + R2) ]


If the answer is Yes then you have a connection problem. If you get a Zs measurement on the RDC input terminals, but not on the RCD output terminals (using the RCD function in both cases) then its the RCD. If you have a Zs measurement on both sides of the RCD then progress through the circuitry until you don't get a Zs measurement. That will tell you where your problem lies.
 
Go back to the beginning. You get a Ze reading between incommers and main earth. I presume this is using the normal Ze measurement. Can you get a Ze measurement between incommers and main earth using the RCD function?

If the answer is No then you have a meter problem. (The only difference is the way your meter is measuring Ze; one way it works, one way it dosn't). Solution: use a calculation for Zs [= Ze + (R1 + R2) ]


If the answer is Yes then you have a connection problem. If you get a Zs measurement on the RDC input terminals, but not on the RCD output terminals (using the RCD function in both cases) then its the RCD. If you have a Zs measurement on both sides of the RCD then progress through the circuitry until you don't get a Zs measurement. That will tell you where your problem lies.

I will give that a go mate. I think I just leave my meter on the no trip function out of habit as nearly everything has rcd's now.
 

Reply to Cant get a Zs reading ? ? ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

  • Question
That 'stranded 2.5mm' was probably imperial 7/.029 which is about 2.9mm2. Which might account for expected readings being different.
Replies
6
Views
416
  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top