Hi
We recently had an 7kW EV charger installed. Due to the consumer unit being situation within the kitchen of our bungalow, the cable needed to be routed across the loft in order to end up next to the drive,
The contract was with a well known brand, who has sub-contracted out the installation work.
I believe it is 6mm SWA that has been used in the loft. The span over the insulation is roughly 9 metres. Prior to the cable being installed by the installer, there as insulation roughly 200mm.
The cable has been clipped to the ceiling rafters, but the loft insulation material has been completely moved to the side for the run. Attached are before and after install photos.
I have tried googling the SWA cable de-rating tables - some are suggesting a derating of 50% for insulation up to 100mm.
Where I got to was 7kW charger = 32 Amps. 6mm cable rated for 53 amps (in air presumably). Clearly, derating the cable down to 26.5 amps is short of the 32amps the charger is capable of using.
Would you expect a thicker cable to have been used in this installation as I really don't want to lose a section of loft insulation? Or, am I fine to move the insulation back into place so that it will be besides and over the cable (as it was prior to install)
I have queried the above from the installer and I am being ignored,
I would really greatful if anyone could provide any thoughts. Are my calculations way off?
Thanks..
We recently had an 7kW EV charger installed. Due to the consumer unit being situation within the kitchen of our bungalow, the cable needed to be routed across the loft in order to end up next to the drive,
The contract was with a well known brand, who has sub-contracted out the installation work.
I believe it is 6mm SWA that has been used in the loft. The span over the insulation is roughly 9 metres. Prior to the cable being installed by the installer, there as insulation roughly 200mm.
The cable has been clipped to the ceiling rafters, but the loft insulation material has been completely moved to the side for the run. Attached are before and after install photos.
I have tried googling the SWA cable de-rating tables - some are suggesting a derating of 50% for insulation up to 100mm.
Where I got to was 7kW charger = 32 Amps. 6mm cable rated for 53 amps (in air presumably). Clearly, derating the cable down to 26.5 amps is short of the 32amps the charger is capable of using.
Would you expect a thicker cable to have been used in this installation as I really don't want to lose a section of loft insulation? Or, am I fine to move the insulation back into place so that it will be besides and over the cable (as it was prior to install)
I have queried the above from the installer and I am being ignored,
I would really greatful if anyone could provide any thoughts. Are my calculations way off?
Thanks..