What allowance for diversity, if any, would you apply to caravan hookup sockets?
The circuit will have just one hookup point, with two 16A sockets. It's a fair distance from the CU, so voltage drop is going to be significant. It would be good to keep the cable CSA down if feasible.
Ok so are you saying that the OP needs to install into the design a circuit that detects flow into the source ?.
Not as yet, since it's relatively new potential problem, that the powers that be haven't cottoned onto yet. Watch this space. Separate earth rods for each point?
Maybe have some sort of sprinkler system as well as a fire alarm and security just in case they have fire arms
If you've ever seen a caravan burn, you'd know that there's little chance for fire fighting once it gets going.
We burnt one at our barbecue a few years ago. Drove everyone10m back across the garden and onto the top of the hedge from the heat.
If the specification says 16A per caravan for every caravan, then you can't apply diversity, what does the spec actually say?
it is primarily up to the designer to establish with the client the types of loads and thus supplies needed.
I would guess each would pull no more than 10Amps for any significant duration.
I would also say you could get away with 5% voltage drop as the lighting is 12v
There's no specification. The customer has told me they want 2 caravan sockets, and told me where they want them, the rest is up to me.
100 mtrs Buried 10mm 2 core swa should give you around 25 amps 4.9% voltage drop.
Like you said, divorce the tncs armour at the hook-up and rod it.
I would also 100ma S type rcd at source if only to protect against the hook-up being damaged and the live supply coming into contact with the TT.
If it’s a “site” to be following the regs for caravan sites, have they also thought of the distance between units for fire regulations?
From memory, all our hookups were factory made. RCD, then a 16A type C… but that was before the regs came in that said every socket had to have its own RCD.
We had RCD, to 2x16’s and a 6 for the light on top of the hookup post.
Even the majority of statics we had didn’t trip a 16A. Except for the ones that had a 4 slice toaster, foreman grill, coffee machine, washing machine, quick boil kettle and the one woman that had her trainee plumber grandson wire in a 9kW electric shower!
This is from the rules I was given for setting up my site.
"In siting hook-ups it is also important to bear in mind that the recommended minimum safety spacing between caravans is 6 metres (20 ft). Each caravan should also have at least 3 metres (10 ft) of clear space surrounding it to restrict the spread of fire."
I'm no expert on selectivity, it's almost never an issue for the type of work I usually do, but I can see the need to get it right in this instance. The general rule of thumb I was taught was 2:1 for breakers, so I figured a B32 upstream, and B16 downstream would do it. Do you think this won't work?
For tripping on the thermal curve during overload that is reasonable enough. The problem is if/when you hit the "instant" magnetic trip point on a hard fault typically you will hit the upstream point as well and both will be past the point of no return by time the downstream MCB has opened.
That is why fuses (with some thermal inertia) or MCCB with a short-term delay (20ms is enough) are preferred as the upstream OCPD for selectivity with MCB/RCBO.
For example, if you look up the Hager tables for 16A B-curve RCBO fed from difference upstream OCPD we have:
  • 32A MCB (B-curve) they are only selective to 150A faults, Zs <= 1.1 ohm
  • 32A MCB (C-curve) to 280A, with Zs <= 0.55 ohm
  • 32A MCB (D-curve) to 460A, with Zs <= 0.55 ohm (5s disconnection)
  • 32A BSS88 fuse would 500A, with Zs <= 1.25 ohm (5s, cold table figure)
  • 32A x160 series MCCB to 1.19kA, with Zs <= 0.68 ohms (5s hot, 0.54 cold)
If you are looking at a TT supply for the SWA or otherwise using a 100mA/300mA delay RCD then 2C is fine and you can also chose the OCPD on the basis of cable adiabatic, not Zs for fault disconnection (as the RCD achieves that). Then your 10mm cable could have a 50A fuse (so selective to 1.4kA) or similar.
However, fuses are a right pain for any unskilled on-site support so if selectivity is that important then coughing up for a MCCB board might well be worth it.
EDIT: Also check what your likely PSCC is at the end of cable. For example if you are looking at around 25A at 5% drop then your max fault current would be around 500A so anything selective to that or higher won't ever have issues (e.g. 32A or so fuse, RCD & 40A D-curve MCB, etc).
The thing that has changed is that the 16A sockets now have to be the switched and interlocked type, which will inevitably lead to damage when customers try to unplug without switching off first.
Just like the one that the OP proposes to use right at the beginning of the thread, so I'm sure he's well aware of that (which you also seem to have a problem with) any suggestions as to how you would do this installation obviously not using a RCD at the source because you have said already that it serves no purpose.
I see that this has basically been discussed before by yourself, and seem to have had a change of heart on certain things.
Don't feel the need to reply, as I think the OP has more than enough info now.
If fault protection is provided by a fuse or circuit breaker then an rcd isn't required.
I understand that one isn't required, but my reasoning for using one would be mainly for a damaged hook up point where the live conductor could come into contact with the TT earth.
Imo if it was a fixed CU and met disconnection times etc then I would have no problem, but these hook-ups are usually just a stake in the ground and there's always going to be the risk of driving off without unplugging.