Caravan hook ups | Page 2 | on ElectriciansForums
Discuss Caravan hook ups in the UK Electrical Forum area at ElectriciansForums.net
Doomed
Dorset
Testing a touring site for the first time - a.n.other has been doing it for years.
Incoming TNCS to glorified shed in field, outputs to hook ups earthed by SWA sheath, not connected to the big metal dis board, terminated in plastic boxes and connected to a rod so is theoretically TT'ed.
However, the readings I was getting at the hook ups seemed too good to be true, so after disconnecting everything from the rod I measured the resistance between the rod and the earth in the dis board (the TNCS earth). Result was 25 ohms.
As I said, the rod was disconnected from ever thing, so logically the resistance was through the ground.
Is this OK?
Also, elsewhere there is a poor connection in the armour between 2 hook ups, not too bad but notable. Is it worth putting another rod at this point.
Just the one rod, but there must be other routes to ground as the readings i'm getting are better at the outlets then the Ra reading.
Went through the clients records today, 2 other companies have signed it off over the last 8 years, its tested annually.
Maybe check to see if there are any earth pits hidden somewhere. Or if there has been extensions to building blocks since the last company came in. Maybe something is hidden. Sounds too good to be true with one rod.
Something is clearly wrong somewhere, there shouldn't be any other routes to ground/earth unless they are made connections. Might be worth conducting some sheath tests if you can't find the source of this 4 to 5 ohms, not that i can see sheath damage (even to every cable) giving you those kind of values. lol!!
Is this OK?
Firstly, you dont test between the rod and the earth.
Cheers
I might have been miss reading this situation, if you are loop testing this single rod with everything disconnected and seeing a Ra value of 4 to 5 ohms, then that's fine. I was under the impression that you were seeing this low Ra value when testing at the hook-up points, with the rod disconnected.
As for testing between the TNC-S and the rod, not sure why you tested this, but all sorts of reasons for this value to be seen, one remote possible reason is the local DNO TNC-S multiple N-E link earth rod location. It could well be quite close-by, especially if the DNO's supply to this caravan park is derived from an overhead supply...
I might have been miss reading this situation, if you are loop testing this single rod with everything disconnected and seeing a Ra value of 4 to 5 ohms, then that's fine. Yep, thats how it is. I was under the impression that you were seeing this low Ra value when testing at the hook-up points, with the rod disconnected. No, these readings were around the same value give or take a few ohms
As for testing between the TNC-S and the rod, not sure why you tested this, I was checking that there was a physical seperation between them, I took a reading between them first before stripping lots of stuff out of the way to confirm visually that there was no connection. but all sorts of reasons for this value to be seen, one remote possible reason is the local DNO TNC-S multiple N-E link earth rod location. It could well be quite close-by, especially if the DNO's supply to this caravan park is derived from an overhead supply...
Thank you
Cheers
Normally I wouldn't, but as the readings I was getting seemed too good to be true I was measuring to see if there was a connection between the TNCS earthing and the TT earthing before I stripped loads of stuff down to confirm a physical disconnection.
Okay, that makes sense now. Well this is one of those times when a really low RA can be problematic in the sense of PME diverted neutral currents.
Have you disconnected the swa earths then tested one by on to see if a particular ciircuit is low?
Cheers
Cheers
That would be difficult in this situation, and as I could visually confirm the separation I have left it. I would of liked to of investigated further but it would of been an academic exercise to satisfy my curiosity, and time constraints did not allow this.
Well if the armour is the cpc, i was thinking there could be a risk of corrosion to exposed armouring/glands.
Cheers
Reply to Caravan hook ups in the UK Electrical Forum area at ElectriciansForums.net