Working in a caravan park as a full time electrician found that most of the hook up point in every single pitch got high Zs reading because of using two core SWA (average 1.7 ohms TNS earthing system). In some cases up to 31ohms because corroded SWA glands and broken SWA. if there's been used 3 core and you wouldn't have many issues with reliable earth for caravan.
now my question is; is there any Regs that contractors have to or must use three core SWA for all caravan park installation. Recently the park I work, all the caravan park installation under ground cable has been upgraded but 2core. I raised this issue to the contractor but never listened and said its fine. I know that SWA can be used as earth but no good for long term due to weather and could corroded glands and SWA then loosing earth continuity or not reliable earth. In many cases I had to replace SWA glands or re-terminate while doing EICR for those caravan.
What do you think guys using 2core SWA in caravan park and in this typical English weather?
now my question is; is there any Regs that contractors have to or must use three core SWA for all caravan park installation. Recently the park I work, all the caravan park installation under ground cable has been upgraded but 2core. I raised this issue to the contractor but never listened and said its fine. I know that SWA can be used as earth but no good for long term due to weather and could corroded glands and SWA then loosing earth continuity or not reliable earth. In many cases I had to replace SWA glands or re-terminate while doing EICR for those caravan.
What do you think guys using 2core SWA in caravan park and in this typical English weather?