Hi I haven't posted for a while but I'm having some issues with a caravan park I have recently carried out some work on and washoping somebody may be able to shed some light on the issue.
The problem is burnt out neutrals on out going side of RCBO, we have replaced 137 caravan suppły points I've the winter and now the camp is back open the problems have started, I have replaced 5 RCBO'S up to now all with the same BADLY burnt out neutral, now I know the obvious answer is loose connection on the neutral but was wondering if any body had come across the same problem with a different cause as we check all manufacturers connections. The supplies have been reduced to only 10amps!! (By instruction of camp owner to reduce electricity consumption as the camp pays for the electricity)
i can't see any overload issues apart from the standard "nuisance tripping" until caravan owners decrease the power they are using. The reason may just be the odd loose neutral but in my 25 years of work I have never seen so many in such a short space of time! Any ideas would be great fully recieved.

Thanks.
 
Quite possibly I'll be carrying out a few resistance test tomorrow on a few random rcds around the site. I'm starting to think this could be a problem with the manufacturer
 
Do you think that the fact that no boot lace ferrules have been used in the boxes by the manufacturer that the fine cores of the fly leads which appear to be spread could cause a high resistance joint??
 
Do you think that the fact that no boot lace ferrules have been used in the boxes by the manufacturer that the fine cores of the fly leads which appear to be spread could cause a high resistance joint??

It wouldn't necessarily cause an increase in resistance, but it can create a significant reduction in CSA at the point of the connection. But it depends on the type and design of the terminal. A cage type terminal such as you get in MCBs and din rail connectors where a flat plate traps the conductor against another plate is unlikely to suffer as much as a standard screw terminal.
 
The terminals are din rail connectors direct into RCBO, no screw terminals are used like we see in neutral bars, surely the decreased csa of the conductor could cause a high resistance taking into account these vans are only on 10amp supplies so are pulling very close to the maximum??
 

Reply to Caravan suppły RCBO in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Get better soon
    • Friendly
    • Like
Replies
10
Views
470
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
751
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Well spotted, and very true Faults can have what I call a "cascade" effect, a mild fault - either a loose connection or a short, say from damaged...
    • Like
2
Replies
19
Views
1K
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top