I am carrying out a refurbishment job on this old panel board and fitting in a new panel board from Schneider. The current supply to this building is a 100amps BS88-2 Gg (assuming). I am planning to protect the outgoing submains with the NSX100 ML 2.2 set at 100 and 63 respectively. I don't know the full load but the current submains have 100Amps MCCBs and 63Amps. For some reason the Schneider quick selectivity tool says there is no selectivity between the upstream 100amps fuse and ML 2.2 but shouldn't it be fine? Here is the picture : ML 2.2 @100 and BS88-2 Fuse.
ML2.2 @63 and BS88-2
Looking at this graphs, the protection device for the submains would trip first before the main fuse.
Any help would be appreciated, thank you.