Carrying out Minor works ! | Page 2 | on ElectriciansForums
Discuss Carrying out Minor works ! in the Talk Electrician area at ElectriciansForums.net
If you look at the definition of an EIC the very first point tells us that it is to be used for an new installation or an addition or alteration where new circuits have been introduced.
So the moving of an existing circuit be it for the sockets or lights will all come under an MEIWC. As it is 2 circuits then you need to do 2 different certs for it.
Now for the sockets you will need to provide RCD protection if you are burying the cables that contravene regulation 5266.6.6 and 526.6.7. As for the sockets themselves, well IMO it's a technical point if your moving 3 sockets say and re-fiting those 3 sockets in just a different location, do you have to provide RCD protection, I suppose technically it should be yes .............
The lighting circuit again will come under the cable regulation and if you contravene it then you will need to provide RCD protection.
What all this work will need though is notifying under Part P
If your adding an RCD it will require a full EIC for the circuit If as you say the full house is fed via the kitchen socket circuit Id personaly rewire and from my understanding of PartPee it IS notifiable as you are al;tering the original
Are you qualified to do this or could the not being qualified be why you are asking questions as to get round certs and notification???? the L.A. building control wont take " I checked with the electricians forum" as an excuse if you get caught out
Quite right Mogga should have added that, yes if you do need to fit RCD protection then as your changing the circuit protection characteristics then an EIC is needed.
If your not fitting RCDs then a MEIWC can be used, as your not changing the circuit characteristics.
From a personal perspective, and reading between the lines,I would plan to do the best job, and not allow a tight budget to influence the standard of work being carried out. Failing that and not knowing the full picture I would at the very least put rcd protected sockets in situ.
Reply to Carrying out Minor works ! in the Talk Electrician area at ElectriciansForums.net
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
It applies to commercial if it shares the same supply as a dwelling.