63a supply to a switch fuse isolator in lift motor room. 63a tp bs88 fuses then 1 meter piece of 5 core 6mm yy flex into lift panel. Anybody know the ccc of the yy cable? Is this a code 2 as I'm sure it's under 63a or no code as it's only 1 meter of cable to the lift panel?
 
you could say it's a fixed load, so the 63A fuses only need to provide fault protection and not overload.
 
Your test finishes at the switch fuse, as you say its a 63amp supply to the switch fuse are the fuses not derated within the switch fuse, the panel may come under a fixed load clause therefore no O/L protection of cable required but that would be for the lift engineer to certify his side of the install..... Im sure by now if the cable was under sized there would be good evidence to show this...

You could check the ELI at the lift panel power terminals and make a comment if it fails but again this is not within your test criteria you stop at the switch fuse and at most comment on any obvious physical damage.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ccc question
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Thread Tags

Tags Tags
question

Advert

Thread statistics

Created
graham123,
Last reply from
Darkwood,
Replies
2
Views
1,044

Advert

Back
Top