G

graham123

63a supply to a switch fuse isolator in lift motor room. 63a tp bs88 fuses then 1 meter piece of 5 core 6mm yy flex into lift panel. Anybody know the ccc of the yy cable? Is this a code 2 as I'm sure it's under 63a or no code as it's only 1 meter of cable to the lift panel?
 
you could say it's a fixed load, so the 63A fuses only need to provide fault protection and not overload.
 
Your test finishes at the switch fuse, as you say its a 63amp supply to the switch fuse are the fuses not derated within the switch fuse, the panel may come under a fixed load clause therefore no O/L protection of cable required but that would be for the lift engineer to certify his side of the install..... Im sure by now if the cable was under sized there would be good evidence to show this...

You could check the ELI at the lift panel power terminals and make a comment if it fails but again this is not within your test criteria you stop at the switch fuse and at most comment on any obvious physical damage.
 

Reply to Ccc question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
540
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
985
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
918

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
603
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
336

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top