The op states it's a Worcester Bosch green star boiler. The thermostat connections on these are 230V not ElV or Volt free. LS provides 230V out for controls and LR is live return.The thermostat connection on the boiler may be low voltage with one leg of the control supply grounded. If this is the case, connecting a neutral at the stat may be causing a problem. I would suggest removing the neutral from the stat and try it again.
The op states it's a Worcester Bosch green star boiler. The thermostat connections on these are 230V not ElV or Volt free. LS provides 230V out for controls and LR is live return.