Hello...
Anyone had any extended experience with ceramic bottle fuse holders.
Shortly after turning on isolator switch there was phase to ground short between one of fuse terminal metallic parts and DIN rail (35A gL/gG fuses have been taken out to test the correct working order of contactors).
MCB with C32 type curve and 6 sqmm conductors tripped as it should.
Might be due to deterioration of dielectric strength or due to close proximity of live metallic components to DIN rail (tight construction). Replaced it with another C32 MCB (only had limited amount of spare ones available).
Will have to put some dedicated motor protection circuit breaker or C25/C20 MCB since the current transformer is only on one phase conductor and with unknown settings on the analogue PLC input.
Anyone had any extended experience with ceramic bottle fuse holders.
Shortly after turning on isolator switch there was phase to ground short between one of fuse terminal metallic parts and DIN rail (35A gL/gG fuses have been taken out to test the correct working order of contactors).
MCB with C32 type curve and 6 sqmm conductors tripped as it should.
Might be due to deterioration of dielectric strength or due to close proximity of live metallic components to DIN rail (tight construction). Replaced it with another C32 MCB (only had limited amount of spare ones available).
Will have to put some dedicated motor protection circuit breaker or C25/C20 MCB since the current transformer is only on one phase conductor and with unknown settings on the analogue PLC input.