Just about to do Garage Supply off a handy FCU on a New Build(TNCS). Nothing big just 2 sockets and lighting.
External Socket already on FCU(on down stairs ring), just running swa from said socket 5 meters in to Garage.
As regards the Installation Cert, the 32A breaker on the board (and RCD)are the origin of the circuit.
Then the Readings at the fittings in the garage (R1+R2, Zs, and Rcd times. IR on ring and spur to garage)
become the installation circuit details.
Or does the 13 amp 1362 become the origin of the garage spur?
Am I over thinking this?
Input greatly appreciated.
Thank you in Advance.
Dave.