say I installed a new cooker cercuit to an existing installation and the customer wants a certificate for the work done do i need to test all the other circuits and record all results for the full instal or just test the circuit I installed and record that also if ther is no main bonding to gas + water do they have to get this installed before certificate can be issued or can I just do a cirtificate for the circuit I installed ? by the way this is a made up Sanorio I’m studying 2391 at college just getting my head around certification
 
You would do an EIC as it is a new circuit. You would just put the circuit that you have installed on it.
If main protective bonding was required, You would need to ensure it was satisfactory.
 
So in this circumstance the customer refuses to pay for bonding to be installed what would be the correct action to take, leeve the new circuit you installed isolated or is it down to the installer to make sure main bonding is in place when installing the cooker circuit?
 
So in this circumstance the customer refuses to pay for bonding to be installed what would be the correct action to take, leeve the new circuit you installed isolated or is it down to the installer to make sure main bonding is in place when installing the cooker circuit?
if customer refuses to pay for earthing/bonding to be installed,then you'd advise that you can't carry out the work. end of.
 
No was goin thru certification an they say if your adding a new cercuit to an existing installation you have to do initial verification but I don’t get if I went to an house say they wanted a new cooker point puttin in so you install the new cercuit then test your work but the EIC requires satafactory bonding but you find the install as no bonding who’s that down to to cuz you have already give a quote for the cooker then you turn around an tell them it’s going to be X amount to install bonding before I can energise the circuit they will be like on ya bike so my question is what do ya do ere lol
 
Just thinking on this . I suppose you could check if the new Cooker can simultaneously be touched together with any extraneous parts. If it is not then technically you have not made the installation any less safe by adding the cooker circuit and bonding is not relevant to the part you have installed. You would need to write that on EIC though and tick N/A for bonding.

Just seen it says you're from Manchester. ...the respectable thing to do would be to take the cash and not issue a cert surely lol ;)
 
Without main protective bonding your new circuit will not fulfil ADS requirements.
 
Before you install ANY circuit to an existing installation, you would check for bonding etc during your initial visit, before you quote for the job or if you quote without doing an initial verification (very unwise), you would check for bonding before you even think about installing the first part of cable.
 
Protective Equipotential Bonding is not required for ADS.
Earthing on the other hand, is required, unless you use an RCD for fault protection.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester

Thread Information

Title
Certificate for additional certificate
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
13

Thread Tags

Advert

Thread statistics

Created
Numb,
Last reply from
Deleted member 26818,
Replies
13
Views
1,726

Advert

Back
Top