Need you're help on issuing a cert. In september last year i did a PIR on a property and all inspection and test results were well within spec.Since then I have recently installed a new CU and on testing i now have a N-E IR fault on the lighting circuit. Out of goodwill and no charge I have spent a day trying to locate the fault and have put this down to a short or cross connection at a JB located within the ceiling etc etc. Just on the IR point all loads dimmers everything possible were disconnected and just to double check a 250V test was also carried out with phases to earth conductors were disconected from the CU main switch isolated. What i want to know is if i can still issue an EIC on completion if the lighting circuit is not protected by an RCD as the owner is not willing to rectify the fault as they are saying i should of known about it???? Any ideas or help greatly appreciated.... Back to the cert can i issue one if so what do i state on it???
 
Your EIC will be limited to 'installation of new consumer unit only' and the fault will be listed in 'comments on the existing installation'.
 
HI THANKS FOR REPLY IS THIS ACCEPTABLE THOUGH AS I HAVE HAD TO FIT THE LIGHTING CIRCUIT TO THE UNPROTECTED SIDE OF THE CU??? wHAT DO I PUT IN THE DETAILS OF DEPARTURES FROM BS7671 2008??
 
You don't put anything under departures.
Unless you intend installing something that departs/doesn't comply, but offers the same degree of safety as would be achieved if you were to comply.
If this fault is existing, then as IQ has already stated, it is just noted on the EIC under comments about the existing installation.
Have you tried putting both lighting circuits on the same RCD to eliminate a possible borowed neutral?
 
HI there is only one lighting circuit supplying the 3 floors, I explained to the owner it would be wise to break the circuit down to cover each floor or at least 2 but not interested same old it worked before!!!.
 
Out of interest what is the IR reading on the faulty circuit? and it sounds like you were lucky installing a high integrity board and having non RCD protected space available.
 
Since then I have recently installed a new CU and on testing i now have a N-E IR fault on the lighting circuit.
So you've already installed the CU?

What is the IR reading you're getting?

If the fault is a low enough resistance to cause RCD tripping (<10k ish) then you cannot finish the job as you will be unable to ensure compliance by connecting the circuit to an RCD (there are bound to be buried cables). You will have to leave the circuit disconnected - or you shouldn't have done the CU change without agreement to rectify.
 
IR Reading is .000 N-E 172 L-N 204 L-E Out of interest what is the IR reading on the faulty circuit? (MURDOCH) and it sounds like you were lucky installing a high integrity board and having non RCD protected space available. HI Integ wylex boards have space for non RCD protected circuits after the main switch???
 
(PC ELECTRICS)If the fault is a low enough resistance to cause RCD tripping (<10k ish) then you cannot finish the job as you will be unable to ensure compliance by connecting the circuit to an RCD (there are bound to be buried cables). You will have to leave the circuit disconnected - or you shouldn't have done the CU change without agreement to rectify. The reason the job got started was previously i had done a pir on the property and all the circuits were within spec,just goes to show a few month down the line and a fault occurs. Conflicting information on certification then can i or cant i
 
Even if the circuits were OK you need to inform your client that faults may be found and costs may be higher.

Did you install a high integrity CU?
 
just goes to show a few month down the line and a fault occurs

Shame you haven't yet diagnosed the fault because imagine if it turned out to be damaged caused by another tradesman that has done work on the property? Obviously when asked I'm sure it would be the sort of thing to slip the owners mind ;)
 
Hi i have been through every switch every light fitting checking resistance,somewhere in the ceiling void there are JB'S as there are no loops on any of the light fittings only 1 T&E to each one. Belive there is a nuetral connected to earth or vice-versa... The question still remains though the owner does'nt want to incur any other cost in fault finding and disruption throughout the property... So am i able to issue a cert??? conflicting information on here ???
 

Reply to certification in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top