Need you're help on issuing a cert. In september last year i did a PIR on a property and all inspection and test results were well within spec.Since then I have recently installed a new CU and on testing i now have a N-E IR fault on the lighting circuit. Out of goodwill and no charge I have spent a day trying to locate the fault and have put this down to a short or cross connection at a JB located within the ceiling etc etc. Just on the IR point all loads dimmers everything possible were disconnected and just to double check a 250V test was also carried out with phases to earth conductors were disconected from the CU main switch isolated. What i want to know is if i can still issue an EIC on completion if the lighting circuit is not protected by an RCD as the owner is not willing to rectify the fault as they are saying i should of known about it???? Any ideas or help greatly appreciated.... Back to the cert can i issue one if so what do i state on it???What's rhe N-E fault IR test results?
 
You really need to come off IR testing range and see what the reading is when set on Ohms as on the IR range it will not read anything under 10000 Ohms it will just give you 0.00

When fault finding this will give you a better idea of where to look on the cct as the nearer the fault the lower the reading will be.
230/0.03 = 7666 Ohms

So if your reading is around that or lower there is a good chance the RCD will not hold.

Hope that makes sense
 

Reply to certification in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top