Certifying mobile container install | on ElectriciansForums

Discuss Certifying mobile container install in the UK Electrical Forum area at ElectriciansForums.net

Ross1

-
Joined
Jan 22, 2011
Messages
366
Reaction score
14
Hi guys, I've completed a new install on a container That's to be sent off to unknown site? 63A commando skt (single phase).

I am to fill in an electrical installation certificate (which I am only able to input dead testing results). Is this correct

if I was to EICR a container the same would apply on that certificate.

many thanks
 
All you can do is the relevant dead test, its upto others on site to carry out the relevant live tests. Would be worth noting this on the EIC that you issue for it so your backside is covered.
 
Add an attachment to the EIC stating the onus of responsibility is on the customer for the on site testing of the relevant listed live electrical tests. You could also note of the need that the same tests are to be carried out at each and every location the mobile container is positioned and connected to an electrical supply in the future.

Probably won't take a blind bit of notice, but your arse is covered from here to doomsday!! lol!!
 
And on the retest date, simply put 'upon energising'. All liability will then be on the customer for the suitability of the supply. Although I would attach a sheet with the cert to recommend what supplies are suitable and ze reading etc


Post no 7.

If you suggest external Z readings you are getting involved in the entire install when the remit was for internal work only.

Any installer worth their salt can do ZS tests to see if the breakers comply with max ZS recommendations. Or, from the individual r1+r2 readings can work out the ZE (ZBD) required to comply
 
Nic cert, simply r1+r2, IR, dead tests, max demand, bs numbers, etc . No ze and zs is available as the building is sent off to the customer. (Probably the other side of the country). Retest is upon energising. This is my bread and butter, company I HAVE worked for is the leader in the market for transportable buildings..... Take it easy lads. Home | Morgan Marine
 

Reply to Certifying mobile container install in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K
  • Question
OLEV is now OZEV, in case you weren't aware. Installing EV equipment is not as straightforward as many might think. There is a Code of Practice...
Replies
2
Views
637
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top