cg,ca,ci,cc
Doh, sorry the tutor did mention Cg. Overlooked that.
Lets try again...
15A / Ca of 0.87
17.24A / Cg of 0.70
24.63A
Don't think Cc applies in this case as the cable is not buried in the ground (but I'm probably wrong).
Now check Table 4D2A.
it's 13A n ot 15, IMO gives 21.35A. so 2.5mm
or, take 2.5mm ref, method C = 27A then multgiply by rating factors. 27 x 0.87 x 0.7 = 16.44, so 2.5mm will handle 13A.
Being wacked with a wet fish excluded, I would say that you maybe right and wrong
Method 4 = A
Method 3 = B
looking at app 4 table 4A2 number 3 = ref method B I think my internal translator got jammed
- I'll just take the money and run :)
all this brain work is causing alcohol starvation, need beer to focus.
ur telling me my exams in 2 hrs eeeek
the answer sheet i have gives the answer as 4mm2 so they have used the IN value (15a)
tele how did you no what to times things by on the industrial board question with the motors and that, just hoppe i dont get one of these types but i bet i do ....
Probably in real life this would not be appropriate, but I doubt for this example you would use the load to find your tabulated current since your final circuit has not been designed to incorporate overload protection.
Mr Pedant
Method 4 = A
Method 3 = B
Are you looking at the BRB or BGB ??
BRB P.261
Method 3 = A
Method 4 = B
But I agree with Tel.... It's beero'clock.
sorry guys but can anyone tell me where in the red book i can look to find out this question An industrial Board supples
- 4 TP motors
- 2 x TP&N motors
- 4 x single phase ring circuits
- 2 x single phase lighting circuits
how many live conductors are there
a)36
b)38
c)40
d)52
anyone know how to work that out ...
- 4 TP motors
- 2 x TP&N motors
a)36
b)38
c)40
d)52
The answer is knowing what a live conductor is, from part 2 definitions and knowing how many live conductors are required for each type of circuit.
The C&G 2382 level 3 assumes a certain level of installation knowledge before you start.
lofty84,
telectrix,