I am looking to change a very old fuse box in my garage. I have attached pics for you all.
I am on route to becomeing a Domestic installer, and hoped i could get some more good advice if poss.

This old fuse box, is supplied from the main house Cu. It is on a 32A breaker. The Main Cu is protected by RCD.

The supply enters the garage from below ground in what looks like armoured cable. (see pic). I would like to change this to a small modern 3 or 4 way Cu, obiously with RCD. I will run a new radial & lighting circuit from the new Cu.

Question, I cannot identify a incomming earth ? All I can see is the Live and Neutral from the end of the Armoured Cable. Is this normal? The old metal box is earthed to a old copper pipe.. but cannot see a route back to the house main earth block?

What are my options here? Am I right to assume I either run a 10mm earth all the way from the garage back to the house Cu, Or install a earthing rod more local to the garage supply ?

I am still learning, so all advice or sugestions very welcome.

ps: Providing I am not running any large or abnormal loads from the garage, this supply from the house (on a 32a MCB) is suitable. I would only ever be plugging in the odd power tool, or running 2 light bulbs.. etc

Thanks!!


:stooge_curly:
 

Attachments

  • Garage DB.jpg
    Garage DB.jpg
    101.8 KB · Views: 170
  • Garage Db1.jpg
    Garage Db1.jpg
    227.3 KB · Views: 149
  • Garage DB2.jpg
    Garage DB2.jpg
    64.9 KB · Views: 136
I have noticed the gas meter is actually only 2 meters from the new proposed installation. The gas has the 10mm cpc running back to the main MET in the house. Is it alright to connect to this from my new garage board earth.

I think this is, as I have identified a path back to the main earth block...?
 
No I am disagreeing with Malcolm.
There is no reason why a conductor cannot both be a CPC and a bonding conductor.
I would personaly rather use the armour as a CPC for the SWA, as that is what it is intended for.
However there is nothing preventing the use of a supplementary conductor, such as the gas bond.
I note from the pictures, that there is a copper pipe whith an earth connection.
What is this pipe for, and is it suitable to be used as a conductor?
 
The old pipe is a disused/empty copper water pipe, that enters back into the main house. I would imagine, this is bonded at some point and also would offer a path back to to MET. ?? I can see that this was used as a bond at some point in the past.

??
 
It appears you have a number of options, use the armour, use the gas bond (if the SWA conductors are 10mm²), use the old water pipe, or a combination of the three.
As there are extraneous-conductive-parts that are bonded back to the house MET, making the garage TT is not really an option.
 
agreed. better than dissociating the garage from the house, as the zone is already extended by the 10mm cable and the disused water pipe.
 
Last edited:
The fact that the old water pipe, the gas and the SWA are all earthed/bonded, would suggest that the equipotential zone is already extended, and judging from the pictures, has been for some time.
Attempting to isolate and separate the zone would IMHO be a nightmare.
 
you can't have undersized earthing and/or bonding conductors, but i've never known an installation not to comply with oversized ones.
 

Reply to Change a old garage fuse board / Earthing question... pic s attached in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
131
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
914
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Replies
7
Views
499
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
678

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top